[TRNSYS-users] Wall thickness in TRNBUILD
David BRADLEY
d.bradley at tess-inc.com
Thu Jul 21 09:11:41 PDT 2022
Volodymyr,
This is a common issue with energy modeling tools and I don't think
that there is a "right" answer. Typically I try to draw the building
using the mid point of the walls. It means that the zone volumes will be
a little on the big side and that the thermal loss area will be a little
bit on the large side. For buildings with very thick walls, that can
become a problem but there are challenges in creating transfer functions
for thick walls anyway. Quite a long time ago I did a building using the
inside dimensions and then again with the outside dimensions. Annually
the energy use was nearly identical between the two; certainly it was
well within the other uncertainties of the modeling assumptions.
kind regards,
David
On 07/21/2022 05:02, Volodymyr Pobuta via TRNSYS-users wrote:
>
> Hello
>
> I am using TRNSYS for the simulation of multizone buildings. I have
> made the CAD model on Sketch Up and I moved on to TRNBUILD to define
> all the construction and window layers. My question is the following:
>
> * The walls imported from Sketch Up do not have a thickness. I have
> multiple adjacent areas, for whom I have defined the construction
> layers as supposed, however, while reading the Multi-Zone Building
> Tutorial, I have noticed that the program only calculates the
> U-value for the layer. Since the equations will need the input
> from the volume of the rooms, how can I be sure that the layers
> are defined properly and that I have the correct volume in the room?
>
> Thank you for your time
>
> Sent from Mail <https://go.microsoft.com/fwlink/?LinkId=550986> for
> Windows
>
> - *AVISO* -
>
> Esta mensagem de correio eletrónico e quaisquer dos seus ficheiros
> anexos, caso existam, são confidenciais e destinados apenas à(s)
> pessoa(s) ou entidade(s) acima referida(s), podendo conter informação
> confidencial, privilegiada, a qual não deverá ser divulgada, copiada,
> gravada ou distribuída nos termos da lei vigente. Se não é o
> destinatário da mensagem, ou se ela lhe foi enviada por engano,
> agradecemos que não faça uso ou divulgação da mesma. Se recebeu esta
> mensagem por engano, por favor avise-nos de imediato, por correio
> eletrónico, para o endereço acima e apague este e-mail do seu sistema.
>
> Obrigado.
>
> - *NOTICE* -
>
> This e-mail transmission and eventual attached files are intended only
> for the use of the individual or entity named above and may contain
> information that is confidential, privileged and exempt from
> disclosure under applicable law. If you are not the intended
> recipient, or if you have received this transmission in error, please
> immediately notify us by e-mail at the above address and delete this
> e-mail from your system.
>
> Thank you.
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220721/f4fbe8e5/attachment.htm>
More information about the TRNSYS-users
mailing list