[TRNSYS-users] Question
Sam Elyas
karaktus at gmail.com
Mon Jun 24 05:40:00 PDT 2019
Hi Aya,
I had to deal with the same issue recently, I used an input and set the
setpoints in order to not have cooling when there is no occupancy. to
achieve that I "26*Occypancy*SeasonC+100*(1-Occupancy*SeasonC)" where
seasonC is the cooling season, Occupancy is an input from type14 (and
41a) schedule.
Hope that helps.
Regards,
Le 24/06/2019 à 09:20, aya khalil via TRNSYS-users a écrit :
>
> Dear ,
> /I trying to calculate the cooling demand of my office // building in
> TRNBUILD and would like the cooling demand to //response according to
> my occupancy schedule(less cooling at //night and more cooling at
> day). I try to define the set temp // at the cooling type by i not
> sure which one should i use /(/schedule or input?) And also the
> equation behind it,// because when i enter like for instance
> _25degree(set temp) //*occupancy schedule+0_, i would get 0 degree
> when there is // no occupancy. // Appreciate your kind assistance on
> this Email /
> /Aya khalil /
> /Master student at usj-beirut /
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190624/f58e676f/attachment.htm>
More information about the TRNSYS-users
mailing list