<p>Hi Aya,</p>
<p>I had to deal with the same issue recently, I used an input and
set the setpoints in order to not have cooling when there is no
occupancy. to achieve that I
"26*Occypancy*SeasonC+100*(1-Occupancy*SeasonC)" where seasonC is
the cooling season, Occupancy is an input from type14 (and 41a)
schedule.</p>
<p>Hope that helps.</p>
<p>Regards,<br>
</p>
<div class="moz-cite-prefix">Le 24/06/2019 à 09:20, aya khalil via
TRNSYS-users a écrit :<br>
</div>
<blockquote type="cite"
cite="mid:BY5PR19MB317497115D6E4F3C50500579E1E00@BY5PR19MB3174.namprd19.prod.outlook.com">
<meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
<br>
Dear ,
<div>
<pre><font face="UICTFontTextStyleBody"><span style="white-space: normal; background-color: rgba(255, 255, 255, 0);"><i> I trying to calculate the cooling demand of my office </i><i> building in TRNBUILD and would like the cooling demand to
</i><i>response according to my occupancy schedule(less cooling at
</i><i>night and more cooling at day). I try to define the set temp
</i><i> at the cooling type by i not sure which one should i use </i>(<i>schedule or input?) And also the equation behind it,</i><i> because when i enter like for instance _25degree(set temp)
</i><i>*occupancy schedule+0_, i would get 0 degree when there is
</i><i> no occupancy.
</i><i> Appreciate your kind assistance on this Email </i></span></font></pre>
<pre><font face="UICTFontTextStyleBody"><span style="white-space: normal; background-color: rgba(255, 255, 255, 0);"><i>Aya khalil </i></span></font></pre>
<pre><font face="UICTFontTextStyleBody"><span style="white-space: normal; background-color: rgba(255, 255, 255, 0);"><i>Master student at usj-beirut </i></span></font></pre>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</body>
</html>