[TRNSYS-users] How to calculate pressure difference(pa)
David BRADLEY
d.bradley at tess-inc.com
Tue Jul 5 09:31:08 PDT 2011
Wang,
It depends on what the pressure difference was during your test!
Typical test data is reported at a 50 Pa pressure difference but if that
isn't what you used when you measured the infiltration rate then this
"typical" value is irrelevant.
David
On 7/5/2011 10:59, 王洋 wrote:
> Dear Mr. Bradley,
> Thanks for your reply!
> I only want to compare the actual measurement value with the
> TRNFlow results. I made an experiment in our test room and got the
> infiltration rate as 0.4 1/h using the tracer gas, but I didn't know
> the pressure difference value between indoor and outdoor at that
> time. Then I used TRNFlow's TEST DATA to set this infiltration rate
> 0.4 and test and compare the TRNFlow result with the actual
> measurement result. As you know, the TEST DATA need the pressure
> difference value between indoor and outdoor. So I asked you about how
> many Pas I should set?
> thanks!
> Br.
> wang
>
> 2011/7/5 David BRADLEY <d.bradley at tess-inc.com
> <mailto:d.bradley at tess-inc.com>>
>
> Wang,
> If you are defining the pressure difference value in the test
> data option then typically you would have the results of a "blower
> door" test in which a special door containing a computer
> controlled fan is installed in the building. The fan is run at
> different speeds to force a pressure difference between indoors
> and outdoors. Running the fan at various speeds can give you an
> estimate of the total leakage area of the building. If you are
> working with a building design (instead of with an actual
> building) then you can't really use the "test data" type of
> opening in TRNFlow. You need to use the more theoretical opening
> types.
> Regards,
> David
>
>
>
> On 7/4/2011 08:14, 王洋 wrote:
>> Dear Mr. Bradley,
>> Thanks for your patient reply!
>> To the pressure difference between indoors and outdoors:
>> Do you mean it's difficult to use some measuring devices and
>> methods to test it? Whether there is no an Maths Equation to
>> calculate this value according to known data e.g. building
>> height, wind spead etc.?
>> Because I need one pressure difference(pa) value in Test Data
>> Option of TRNFLOW.
>> Many thanks!
>> br.
>> wang
>>
>>
>> 2011/7/1 王洋 <wanghongyang1767 at gmail.com
>> <mailto:wanghongyang1767 at gmail.com>>
>>
>>
>> 2011/3/16 David BRADLEY <d.bradley at tess-inc.com
>> <mailto:d.bradley at tess-inc.com>>
>>
>> Wang,
>> Chapter 18 is the one you need; look specifically on
>> page 18.19 at the mathematical description of the
>> conduction process through the walls.
>>
>> As for your question about pressure differences, the
>> pressure difference between indoors and outdoors varies
>> with a great many factors (windspeed, direction,
>> obstructions, building height, the nature of the openings
>> in the building facades, etc.). In many tests, the flow
>> through an opening with a 50Pa pressure difference is
>> given. Whether a 50Pa pressure difference is average or
>> extreme, however, depends on the building.
>> Regards,
>> David
>>
>>
>>
>> On 3/16/2011 08:25, 王洋 wrote:
>>>
>>>
>>> Dear Mr. Bradley,
>>>
>>> But I cann't find the ASHRAE Handbook of
>>> Fundamentals about
>>> the Conduction Transfer Function methodology. My
>>> ASHRAE Handbook of Fundamentals is 2009 version.
>>> The chapter 4 Heat transfer and Chapter 6 Mass transfer
>>> have no informations about transfer function coefficients.
>>> Please tell me which chapter of the ASHRAE Handbook of
>>> Fundamentals contains transfer function coefficients etc.?
>>>
>>> PLUS: In Test Data Option of TRNFLOW : about the
>>> pressure difference(pa). Please tell me normally what's
>>> the pressure differnce between outside and inside in
>>> winter or summer? The trnflow manual and Example
>>> Rest_com.tpf have no detailed introduction. I tried also
>>> 20 pa or 0 pa etc. Is it OK?
>>>
>>> Many thanks!
>>>
>>> Br.
>>>
>>> wang
>>>
>>>
>>>
>>>
>>>
>>> >
>>> >
>>> > Wang,
>>> > The thermal time constant for a zone in your
>>> building is not a simple
>>> > thing to compute. It has to do with the materials in
>>> the wall, the
>>> > placement
>>> > of the mass within the wall, the capacitance of the
>>> zone, ventilation,
>>> > infiltration, gains, solar radiation, etc. I would
>>> think that the easiest
>>> > way to get an estimate of the zone's thermal time
>>> constant is to impose a
>>> > step change in one input on it - step change the
>>> ambient temperature while
>>> > holding all other inputs constant for example.
>>> >
>>> > The numbers that you see in the *.inf file are
>>> transfer function
>>> > coefficients. You can read in the ASHRAE Handbook of
>>> Fundamentals about
>>> > the
>>> > Conduction Transfer Function methodology.
>>> > Regards,
>>> > David
>>> >
>>> >
>>> >
>>> > On 11/3/2010 09:29, 王洋 wrote:
>>> >
>>> > Dear all,
>>> >
>>> > 1. How to calculate or find the thermal time constant
>>> of zone in TRNSYS
>>> > software?
>>> >
>>> > ---------- WALL TYPE BST_FL_HEAT_W1 ----------
>>> >
>>> > THERMAL CONDUCTANCE, U= 67.80000 kJ/h m2K;
>>> U-Wert= 4.48235
>>> > W/m2K
>>> > (incl. alpha_i=7.7 W/m^2 K and
>>> alpha_o=25 W/m^2 K)
>>> >
>>> > TRANSFERFUNCTION COEFFICIENTS
>>> > K A B C
>>> D
>>> >
>>> > 0 1.7050117E+02 2.1087019E+01 1.7050117E+02
>>> > 1.0000000E+00
>>> > 1 -1.1800059E+02 3.5808933E+01 -1.1800059E+02
>>> > -1.3683139E-01
>>> > 2 6.0267372E+00 1.6298573E+00 6.0267372E+00
>>> > 4.7362566E-05
>>> > 3 -1.2736107E-03 2.3363784E-04 -1.2736107E-03
>>> > SUM 5.8526043E+01 5.8526043E+01 5.8526043E+01
>>> > 8.6321597E-01
>>> > What's meaning of A B C D? Are they Wall's
>>> TRANSFERFUNCTION COEFFICIENTS?
>>> > And what is the thermal time constant of the whole
>>> zone? How to calculate
>>> > or
>>> > find the thermal time constant of the whole zone in
>>> TRNSYS software?
>>> > Need I calculate by myself the whole zone's
>>> TRANSFERFUNCTION based on
>>> > all
>>> > the walls of the zone or others?
>>> >
>>> > 2. How to calculate or find air volume flow of the
>>> window opening in
>>> > TRNFlow software?
>>> > The window opening area (m2)is known. Whether it
>>> needs the wind
>>> > speed(m/s)
>>> > or not?
>>> >
>>> > Many thanks!
>>> >
>>> > Br.
>>> >
>>> > wang
>>> > 2010/11/3 <trnsys-users-request at cae.wisc.edu
>>> <mailto:trnsys-users-request at cae.wisc.edu>>
>>> >
>>> >> Send TRNSYS-users mailing list submissions to
>>> >> trnsys-users at cae.wisc.edu
>>> <mailto:trnsys-users at cae.wisc.edu>
>>> >>
>>> >> To subscribe or unsubscribe via the World Wide Web, visit
>>> >>
>>> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >> or, via email, send a message with subject or body
>>> 'help' to
>>> >> trnsys-users-request at cae.wisc.edu
>>> <mailto:trnsys-users-request at cae.wisc.edu>
>>> >>
>>> >> You can reach the person managing the list at
>>> >> trnsys-users-owner at cae.wisc.edu
>>> <mailto:trnsys-users-owner at cae.wisc.edu>
>>> >>
>>> >> When replying, please edit your Subject line so it is
>>> more specific
>>> >> than "Re: Contents of TRNSYS-users digest..."
>>> >>
>>> >> Today's Topics:
>>> >>
>>> >> 1. Re: GenOpt optimization: problem for the second
>>> generation
>>> >> after 5 simulations (Thibaut VITTE)
>>> >> 2. Re: google sketchup+trnsys3d (hotline)
>>> >> 3. input file (Emiliano Casati - 3ME)
>>> >> 4. Re: GenOpt optimization: problem for the
>>> secondgeneration
>>> >> after 5 simulations (Timothy McDowell)
>>> >>
>>> >>
>>> >> ---------- 已转发邮件 ----------
>>> >> From: Thibaut VITTE <thibaut.vitte at h3c-energies.fr
>>> <mailto:thibaut.vitte at h3c-energies.fr>>
>>> >> To: trnsys-users at cae.wisc.edu
>>> <mailto:trnsys-users at cae.wisc.edu>
>>> >> Date: Wed, 03 Nov 2010 11:27:53 +0100
>>> >> Subject: Re: [TRNSYS-users] GenOpt optimization:
>>> problem for the second
>>> >> generation after 5 simulations
>>> >> Dear Alexis,
>>> >>
>>> >> I've had a similar error when I used Genopt. I've had
>>> several components
>>> >> tracked by a "trace" command that made my list file
>>> enormous (more than
>>> >> 100Mb) and genopt could'nt handle that amount of data.
>>> >>
>>> >> Just my 2cents.
>>> >>
>>> >> Thibaut
>>> >> --
>>> >>
>>> >> Le futur maîtrisé
>>> >>
>>> >> Thibaut VITTE
>>> >>
>>> >> Docteur - Ingénieur Energies
>>> >>
>>> >> Mail : thibaut.vitte at h3c-energies.fr
>>> <mailto:thibaut.vitte at h3c-energies.fr>
>>> >>
>>> >> -----------------------------
>>> >>
>>> >> H3C-énergies
>>> >>
>>> >> 35, chemin du vieux Chêne - 38240 MEYLAN
>>> >>
>>> >> Tél : 04 76 41 88 66 – Fax : 04 76 41 28 94
>>> >>
>>> >> www.h3c-energies.fr <http://www.h3c-energies.fr/>
>>> >>
>>> >>
>>> >>
>>> -----------------------------------------------------------------------------------
>>> >>
>>> >> Afin de contribuer au respect de l'environnement,
>>> merci de n'imprimer ce
>>> >> message qu'en cas de nécessité.
>>> >>
>>> >> In order to respect the environment, please don't
>>> print this e-mail
>>> >> unless
>>> >> you really need to.
>>> >>
>>> >>
>>> >> ---------- 已转发邮件 ----------
>>> >> From: "hotline" <hotline at transsolar.com
>>> <mailto:hotline at transsolar.com>>
>>> >> To: "julia.feste" <julia.feste at whitepavilion.com.cn
>>> <mailto:julia.feste at whitepavilion.com.cn>>
>>> >> Date: Wed, 3 Nov 2010 11:37:08 +0100
>>> >> Subject: Re: [TRNSYS-users] google sketchup+trnsys3d
>>> >> Hi,
>>> >>
>>> >> that's a well known problem that will be fixed in the
>>> next version.
>>> >> Hopefully upcoming within the next weeks.
>>> >>
>>> >> Regards
>>> >> Christian
>>> >>
>>> >> TRANSSOLAR Software Team
>>> >> hotline at transsolar.com <mailto:hotline at transsolar.com>
>>> >>
>>> >> www.trnsys.de <http://www.trnsys.de/>
>>> >> Transsolar KlimaEngineering - Technologien für
>>> energieeffizientes Bauen
>>> >> und Nutzerkomfort in Gebäuden
>>> >> Transsolar Energietechnik GmbH, Curiestrasse 2, 70563
>>> Stuttgart /
>>> >> Amtsgericht Stuttgart - HRB 23347 / USt-IdNr.:
>>> 99073/00911
>>> >> Geschäftsführer: Dipl.Ing. Matthias Schuler,
>>> Dipl.Ing. Thomas Auer,
>>> >> Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher
>>> >>
>>> >> -----Ursprüngliche Nachricht-----
>>> >> Von: julia.feste
>>> [mailto:julia.feste at whitepavilion.com.cn
>>> <mailto:julia.feste at whitepavilion.com.cn>]
>>> >> Gesendet: Mittwoch, 3. November 2010 06:46
>>> >> An: trnsys-users at cae.wisc.edu
>>> <mailto:trnsys-users at cae.wisc.edu>
>>> >> Betreff: [TRNSYS-users] google sketchup+trnsys3d
>>> >>
>>> >>
>>> >> Hello everybody,
>>> >> Thanks for your posts that's always really interesting!
>>> >> I come up with a problem using Google Sketchup and
>>> TRNSYS3D: inside a
>>> >> TRNSYS zone, I draft a square, then I want to pull it
>>> up at a certain
>>> >> height, so I write the number then Enter, and this
>>> error appears:
>>> >>
>>> >> <-----Beginning of the error----->
>>> >> ERROR:
>>> >> NoMethodError
>>> >> undefined method `position' for
>>> >> #<Sketchup::AttributeDictionary:0xfcb4eb8>
>>> >>
>>> >> BACKTRACE:
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in
>>> `polygon_loop'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `each'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in
>>> `polygon_loop'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:321:in
>>> `outer_polygon'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:326:in `polygon'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:27:in
>>> >> `detect_base_face'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >>
>>> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in
>>> `each'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in
>>> >> `detect_base_face'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >>
>>> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:254:in
>>> `face_polygon'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >>
>>> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in
>>> `each'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >>
>>> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in
>>> `face_polygon'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/Surface.rb:107:in
>>> >> `update_input_object'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:94:in
>>> >> `update_input_object'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >>
>>> 8/Plugins/Trnsys3d/lib/interfaces/DrawingInterface.rb:353:in
>>> >> `on_change_entity'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >>
>>> 8/Plugins/Trnsys3d/lib/observers/FaceObserver.rb:32:in
>>> `onChangeEntity'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/AsynchProc.rb:17:in `initialize'
>>> >>
>>> >> <-----End of the error----->
>>> >>
>>> >> When I pull it up manual, I don't have any problem,
>>> just when I write
>>> >> the number.
>>> >>
>>> >> Thanks in advance for your help,
>>> >> Julia.
>>> >> ________________________________________
>>> >> From: trnsys-users-request at cae.wisc.edu
>>> <mailto:trnsys-users-request at cae.wisc.edu>
>>> >> [trnsys-users-request at cae.wisc.edu
>>> <mailto:trnsys-users-request at cae.wisc.edu>]
>>> >> Sent: Wednesday, November 03, 2010 1:04 AM
>>> >> To: trnsys-users at cae.wisc.edu
>>> <mailto:trnsys-users at cae.wisc.edu>
>>> >> Subject: TRNSYS-users Digest, Vol 71, Issue 4
>>> >>
>>> >> Send TRNSYS-users mailing list submissions to
>>> >> trnsys-users at cae.wisc.edu
>>> <mailto:trnsys-users at cae.wisc.edu>
>>> >>
>>> >> To subscribe or unsubscribe via the World Wide Web, visit
>>> >>
>>> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >> or, via email, send a message with subject or body
>>> 'help' to
>>> >> trnsys-users-request at cae.wisc.edu
>>> <mailto:trnsys-users-request at cae.wisc.edu>
>>> >>
>>> >> You can reach the person managing the list at
>>> >> trnsys-users-owner at cae.wisc.edu
>>> <mailto:trnsys-users-owner at cae.wisc.edu>
>>> >>
>>> >> When replying, please edit your Subject line so it is
>>> more specific than
>>> >> "Re: Contents of TRNSYS-users digest..."
>>> >>
>>> >> _______________________________________________
>>> >> TRNSYS-users mailing list
>>> >> TRNSYS-users at cae.wisc.edu
>>> <mailto:TRNSYS-users at cae.wisc.edu>
>>> >>
>>> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> ---------- 已转发邮件 ----------
>>> >> From: "Emiliano Casati - 3ME"
>>> <E.I.M.Casati at tudelft.nl <mailto:E.I.M.Casati at tudelft.nl>>
>>> >> To: <trnsys-users at cae.wisc.edu
>>> <mailto:trnsys-users at cae.wisc.edu>>
>>> >> Date: Wed, 3 Nov 2010 13:19:58 +0100
>>> >> Subject: [TRNSYS-users] input file
>>> >>
>>> >> Hi to everybody!
>>> >>
>>> >> I don’t understand why, for certain projects, I can’t
>>> open the input
>>> >> file,
>>> >> the message is “the system cannot find the path
>>> specified”.
>>> >>
>>> >> Where should I find the input file?
>>> >>
>>> >>
>>> >>
>>> >> Thanks a lot
>>> >>
>>> >>
>>> >>
>>> >> ec
>>> >>
>>> >>
>>> >> ---------- 已转发邮件 ----------
>>> >> From: "Timothy McDowell" <mcdowell at tess-inc.com
>>> <mailto:mcdowell at tess-inc.com>>
>>> >> To: "Thibaut VITTE" <thibaut.vitte at h3c-energies.fr
>>> <mailto:thibaut.vitte at h3c-energies.fr>>,
>>> >> trnsys-users at cae.wisc.edu
>>> <mailto:trnsys-users at cae.wisc.edu>
>>> >> Date: Wed, 3 Nov 2010 07:23:05 -0500 (CDT)
>>> >> Subject: Re: [TRNSYS-users] GenOpt optimization:
>>> problem for the
>>> >> secondgeneration after 5 simulations
>>> >> This type of error in GenOpt is usually caused by an
>>> error in the TRNSYS
>>> >> simulation. You need to check the *.lst file for the
>>> TRNSYS run to see
>>> >> what the TRNSYS error is.
>>> >>
>>> >> Regards,
>>> >>
>>> >> Tim
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> ----------------------------------
>>> >> Timothy McDowell
>>> >> Executive Vice President
>>> >> Thermal Energy System Specialists, LLC
>>> >> 22 N. Carroll St, Suite 370
>>> >> Madison, WI 53703
>>> >> Phone: 608-274-2577
>>> >> Fax: 608-278-1475
>>> >>
>>> >> ----- Original Message -----
>>> >> From: "Thibaut VITTE" <thibaut.vitte at h3c-energies.fr
>>> <mailto:thibaut.vitte at h3c-energies.fr>>
>>> >> Sent: Wed, November 3, 2010 5:27
>>> >> Subject:Re: [TRNSYS-users] GenOpt optimization:
>>> problem for the
>>> >> secondgeneration after 5 simulations
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> Dear Alexis,
>>> >>
>>> >> I've had a similar error when I used Genopt. I've
>>> had several
>>> >> components tracked by a "trace" command that made
>>> my list file
>>> >> enormous (more than 100Mb) and genopt could'nt
>>> handle that amount of
>>> >> data.
>>> >>
>>> >> Just my 2cents.
>>> >>
>>> >> Thibaut
>>> >> --
>>> >>
>>> >>
>>> >> .bodyclass @page { size: 8.5in 11in; margin-top:
>>> 0.7874in;
>>> >> margin-bottom:
>>> >> 0.7874in; margin-left: 0.7874in; margin-right: 0.7874in }
>>> >> .bodyclass table { border-collapse:collapse;
>>> border-spacing:0;
>>> >> empty-cells:show }
>>> >> .bodyclass td, th { vertical-align:top;
>>> font-size:12pt;}
>>> >> .bodyclass h1, h2, h3, h4, h5, h6 { clear:both }
>>> >> .bodyclass ol, ul { margin:0; padding:0;}
>>> >> .bodyclass li { list-style: none; margin:0;
>>> padding:0;}
>>> >> .bodyclass li span.odfLiEnd { clear: both;
>>> line-height:0; width:0;
>>> >> height:0; margin:0; padding:0; }
>>> >> .bodyclass span.footnodeNumber {
>>> padding-right:1em; }
>>> >> .bodyclass * { margin:0; }
>>> >> .bodyclass .fr1 { font-size:12pt; text-align:center;
>>> >> vertical-align:top;
>>> >> margin-left:0in; margin-right:0in; margin-top:0in;
>>> margin-bottom:0in;
>>> >> padding:0in; border-style:none; }
>>> >> .bodyclass .P1 { font-size:12pt;
>>> margin-bottom:0in; margin-top:0in;
>>> >> font-family:Times New Roman; text-align:center !
>>> important; }
>>> >> .bodyclass .P10 { font-size:7.5pt;
>>> margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify !
>>> important;
>>> >> color:#f79646; }
>>> >> .bodyclass .P2 { font-size:9pt;
>>> margin-bottom:0in; margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:center !
>>> important;
>>> >> color:#e36c0a; font-style:italic; font-weight:bold; }
>>> >> .bodyclass .P3 { font-size:9pt;
>>> margin-bottom:0in; margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify !
>>> important;
>>> >> color:#e36c0a; font-weight:bold; }
>>> >> .bodyclass .P4 { font-size:9pt;
>>> margin-bottom:0in; margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify !
>>> important;
>>> >> color:#e36c0a; font-weight:bold; }
>>> >> .bodyclass .P5 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; color:#e36c0a;
>>> font-weight:bold; }
>>> >> .bodyclass .P6 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify !
>>> important;
>>> >> color:#3329b1; }
>>> >> .bodyclass .P61 { font-size:8.5pt;
>>> margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify !
>>> important;
>>> >> color:#3329b1; }
>>> >> .bodyclass .P7 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify !
>>> important;
>>> >> color:#3329b1; font-style:italic; }
>>> >> .bodyclass .P8 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify !
>>> important;
>>> >> color:#3329b1; font-style:italic; }
>>> >> .bodyclass .P9 { font-size:12pt;
>>> margin-bottom:0in; margin-top:0in;
>>> >> font-family:Times New Roman; text-align:justify !
>>> important; }
>>> >> .bodyclass .P91 { font-size:12pt; margin-bottom:0in;
>>> >> margin-top:0.05in;
>>> >> font-family:Times New Roman; text-align:justify !
>>> important; }
>>> >> .bodyclass .Standard { font-size:12pt;
>>> font-family:Times New Roman;
>>> >> }
>>> >> .bodyclass .T1 { color:#f79646; }
>>> >> .bodyclass .T2 { color:#f79646;
>>> font-family:Tahoma, sans-serif;
>>> >> font-size:7.5pt; }
>>> >> .bodyclass .T3 { color:#3329b1;
>>> font-family:Tahoma, sans-serif;
>>> >> font-size:7.5pt; }
>>> >> .bodyclass { }
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> Le futur maîtrisé
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> Thibaut VITTE
>>> >> Docteur - Ingénieur Energies
>>> >> Mail : thibaut.vitte at h3c-energies.fr
>>> <mailto:thibaut.vitte at h3c-energies.fr>
>>> >>
>>> >> -----------------------------
>>> >> H3C-énergies
>>> >> 35, chemin du vieux Chêne - 38240 MEYLAN
>>> >> Tél : 04 76 41 88 66 – Fax : 04 76 41 28
>>> >> 94
>>> >> www.h3c-energies.fr <http://www.h3c-energies.fr/>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> -----------------------------------------------------------------------------------
>>> >> Afin de contribuer au respect de l'environnement,
>>> >> merci de n'imprimer ce message qu'en cas de
>>> nécessité.
>>> >> In order to respect the environment, please don't
>>> >> print this e-mail unless you really need to.
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> _______________________________________________
>>> >> TRNSYS-users mailing list
>>> >> TRNSYS-users at cae.wisc.edu
>>> <mailto:TRNSYS-users at cae.wisc.edu>
>>> >>
>>> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >>
>>> >>
>>> >> ----- End of original message -----
>>> >>
>>> >>
>>> >>
>>> >> _______________________________________________
>>> >> TRNSYS-users mailing list
>>> >> TRNSYS-users at cae.wisc.edu
>>> <mailto:TRNSYS-users at cae.wisc.edu>
>>> >>
>>> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >>
>>> >>
>>> >
>>> > _______________________________________________
>>> > TRNSYS-users mailing
>>>
>>> > listTRNSYS-users at cae.wisc.eduhttps://
>>> <mailto:listTRNSYS-users at cae.wisc.eduhttps://>www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> <http://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users>
>>> >
>>> >
>>> > --
>>> > ***************************
>>> > David BRADLEY
>>> > Principal
>>> > Thermal Energy Systems Specialists, LLC
>>> > 22 North Carroll Street - suite 370
>>> > Madison, WI 53703 USA
>>> >
>>> > P:+1.608.274.2577
>>> > F:+1.608.278.1475d.bradley at tess-inc.com
>>> <mailto:F%3A%2B1.608.278.1475d.bradley at tess-inc.com>
>>> > http://www.tess-inc.comhttp://
>>> <http://www.tess-inc.comhttp//>www.trnsys.com
>>> <http://www.trnsys.com/>
>>> >
>>>
>>>
>>>
>>
>> --
>> ***************************
>> David BRADLEY
>> Principal
>> Thermal Energy Systems Specialists, LLC
>> 22 North Carroll Street - suite 370
>> Madison, WI 53703 USA
>>
>> P:+1.608.274.2577
>> F:+1.608.278.1475
>> d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>> http://www.tess-inc.com <http://www.tess-inc.com/>
>> http://www.trnsys.com <http://www.trnsys.com/>
>>
>>
>>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>
> http://www.tess-inc.com <http://www.tess-inc.com/>
> http://www.trnsys.com <http://www.trnsys.com/>
>
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com