[TRNSYS-users] How to calculate pressure difference(pa)
王洋
wanghongyang1767 at gmail.com
Tue Jul 5 08:59:11 PDT 2011
Dear Mr. Bradley,
Thanks for your reply!
I only want to compare the actual measurement value with the TRNFlow
results. I made an experiment in our test room and got the infiltration rate
as 0.4 1/h using the tracer gas, but I didn't know the pressure difference
value between indoor and outdoor at that time. Then I used TRNFlow's TEST
DATA to set this infiltration rate 0.4 and test and compare the TRNFlow
result with the actual measurement result. As you know, the TEST DATA need
the pressure difference value between indoor and outdoor. So I asked you
about how many Pas I should set?
thanks!
Br.
wang
2011/7/5 David BRADLEY <d.bradley at tess-inc.com>
> **
> Wang,
> If you are defining the pressure difference value in the test data option
> then typically you would have the results of a "blower door" test in which a
> special door containing a computer controlled fan is installed in the
> building. The fan is run at different speeds to force a pressure difference
> between indoors and outdoors. Running the fan at various speeds can give you
> an estimate of the total leakage area of the building. If you are working
> with a building design (instead of with an actual building) then you can't
> really use the "test data" type of opening in TRNFlow. You need to use the
> more theoretical opening types.
> Regards,
> David
>
>
>
> On 7/4/2011 08:14, 王洋 wrote:
>
> Dear Mr. Bradley,
>
> Thanks for your patient reply!
>
> To the pressure difference between indoors and outdoors:
> Do you mean it's difficult to use some measuring devices and methods to
> test it? Whether there is no an Maths Equation to calculate this value
> according to known data e.g. building height, wind spead etc.?
>
> Because I need one pressure difference(pa) value in Test Data Option of
> TRNFLOW.
>
> Many thanks!
>
> br.
>
> wang
>
>
> 2011/7/1 王洋 <wanghongyang1767 at gmail.com>
>
>>
>>
>> 2011/3/16 David BRADLEY <d.bradley at tess-inc.com>
>>
>>> Wang,
>>> Chapter 18 is the one you need; look specifically on page 18.19 at the
>>> mathematical description of the conduction process through the walls.
>>>
>>> As for your question about pressure differences, the pressure difference
>>> between indoors and outdoors varies with a great many factors (windspeed,
>>> direction, obstructions, building height, the nature of the openings in the
>>> building facades, etc.). In many tests, the flow through an opening with a
>>> 50Pa pressure difference is given. Whether a 50Pa pressure difference is
>>> average or extreme, however, depends on the building.
>>> Regards,
>>> David
>>>
>>>
>>>
>>> On 3/16/2011 08:25, 王洋 wrote:
>>>
>>>
>>>
>>> Dear Mr. Bradley,
>>>
>>> But I cann't find the ASHRAE Handbook of Fundamentals about
>>> the Conduction Transfer Function methodology. My ASHRAE Handbook of
>>> Fundamentals is 2009 version.
>>> The chapter 4 Heat transfer and Chapter 6 Mass transfer have no
>>> informations about transfer function coefficients.
>>> Please tell me which chapter of the ASHRAE Handbook of Fundamentals
>>> contains transfer function coefficients etc.?
>>>
>>> PLUS: In Test Data Option of TRNFLOW : about the pressure
>>> difference(pa). Please tell me normally what's the pressure differnce
>>> between outside and inside in winter or summer? The trnflow manual and
>>> Example Rest_com.tpf have no detailed introduction. I tried also 20 pa
>>> or 0 pa etc. Is it OK?
>>>
>>> Many thanks!
>>>
>>> Br.
>>>
>>> wang
>>>
>>>
>>>
>>>
>>>
>>> >
>>> >
>>> > Wang,
>>> > The thermal time constant for a zone in your building is not a simple
>>> > thing to compute. It has to do with the materials in the wall, the
>>> > placement
>>> > of the mass within the wall, the capacitance of the zone, ventilation,
>>> > infiltration, gains, solar radiation, etc. I would think that the
>>> easiest
>>> > way to get an estimate of the zone's thermal time constant is to impose
>>> a
>>> > step change in one input on it - step change the ambient temperature
>>> while
>>> > holding all other inputs constant for example.
>>> >
>>> > The numbers that you see in the *.inf file are transfer function
>>> > coefficients. You can read in the ASHRAE Handbook of Fundamentals about
>>> > the
>>> > Conduction Transfer Function methodology.
>>> > Regards,
>>> > David
>>> >
>>> >
>>> >
>>> > On 11/3/2010 09:29, 王洋 wrote:
>>> >
>>> > Dear all,
>>> >
>>> > 1. How to calculate or find the thermal time constant of zone in TRNSYS
>>> > software?
>>> >
>>> > ---------- WALL TYPE BST_FL_HEAT_W1 ----------
>>> >
>>> > THERMAL CONDUCTANCE, U= 67.80000 kJ/h m2K; U-Wert=
>>> 4.48235
>>> > W/m2K
>>> > (incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
>>> >
>>> > TRANSFERFUNCTION COEFFICIENTS
>>> > K A B C D
>>> >
>>> > 0 1.7050117E+02 2.1087019E+01 1.7050117E+02
>>> > 1.0000000E+00
>>> > 1 -1.1800059E+02 3.5808933E+01 -1.1800059E+02
>>> > -1.3683139E-01
>>> > 2 6.0267372E+00 1.6298573E+00 6.0267372E+00
>>> > 4.7362566E-05
>>> > 3 -1.2736107E-03 2.3363784E-04 -1.2736107E-03
>>> > SUM 5.8526043E+01 5.8526043E+01 5.8526043E+01
>>> > 8.6321597E-01
>>> > What's meaning of A B C D? Are they Wall's TRANSFERFUNCTION
>>> COEFFICIENTS?
>>> > And what is the thermal time constant of the whole zone? How to
>>> calculate
>>> > or
>>> > find the thermal time constant of the whole zone in TRNSYS software?
>>> > Need I calculate by myself the whole zone's TRANSFERFUNCTION based on
>>> > all
>>> > the walls of the zone or others?
>>> >
>>> > 2. How to calculate or find air volume flow of the window opening in
>>> > TRNFlow software?
>>> > The window opening area (m2)is known. Whether it needs the wind
>>> > speed(m/s)
>>> > or not?
>>> >
>>> > Many thanks!
>>> >
>>> > Br.
>>> >
>>> > wang
>>> > 2010/11/3 <trnsys-users-request at cae.wisc.edu>
>>> >
>>> >> Send TRNSYS-users mailing list submissions to
>>> >> trnsys-users at cae.wisc.edu
>>> >>
>>> >> To subscribe or unsubscribe via the World Wide Web, visit
>>> >> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >> or, via email, send a message with subject or body 'help' to
>>> >> trnsys-users-request at cae.wisc.edu
>>> >>
>>> >> You can reach the person managing the list at
>>> >> trnsys-users-owner at cae.wisc.edu
>>> >>
>>> >> When replying, please edit your Subject line so it is more specific
>>> >> than "Re: Contents of TRNSYS-users digest..."
>>> >>
>>> >> Today's Topics:
>>> >>
>>> >> 1. Re: GenOpt optimization: problem for the second generation
>>> >> after 5 simulations (Thibaut VITTE)
>>> >> 2. Re: google sketchup+trnsys3d (hotline)
>>> >> 3. input file (Emiliano Casati - 3ME)
>>> >> 4. Re: GenOpt optimization: problem for the secondgeneration
>>> >> after 5 simulations (Timothy McDowell)
>>> >>
>>> >>
>>> >> ---------- 已转发邮件 ----------
>>> >> From: Thibaut VITTE <thibaut.vitte at h3c-energies.fr>
>>> >> To: trnsys-users at cae.wisc.edu
>>> >> Date: Wed, 03 Nov 2010 11:27:53 +0100
>>> >> Subject: Re: [TRNSYS-users] GenOpt optimization: problem for the
>>> second
>>> >> generation after 5 simulations
>>> >> Dear Alexis,
>>> >>
>>> >> I've had a similar error when I used Genopt. I've had several
>>> components
>>> >> tracked by a "trace" command that made my list file enormous (more
>>> than
>>> >> 100Mb) and genopt could'nt handle that amount of data.
>>> >>
>>> >> Just my 2cents.
>>> >>
>>> >> Thibaut
>>> >> --
>>> >>
>>> >> Le futur maîtrisé
>>> >>
>>> >> Thibaut VITTE
>>> >>
>>> >> Docteur - Ingénieur Energies
>>> >>
>>> >> Mail : thibaut.vitte at h3c-energies.fr
>>> >>
>>> >> -----------------------------
>>> >>
>>> >> H3C-énergies
>>> >>
>>> >> 35, chemin du vieux Chêne - 38240 MEYLAN
>>> >>
>>> >> Tél : 04 76 41 88 66 – Fax : 04 76 41 28 94
>>> >>
>>> >> www.h3c-energies.fr
>>> >>
>>> >>
>>> >>
>>> -----------------------------------------------------------------------------------
>>> >>
>>> >> Afin de contribuer au respect de l'environnement, merci de n'imprimer
>>> ce
>>> >> message qu'en cas de nécessité.
>>> >>
>>> >> In order to respect the environment, please don't print this e-mail
>>> >> unless
>>> >> you really need to.
>>> >>
>>> >>
>>> >> ---------- 已转发邮件 ----------
>>> >> From: "hotline" <hotline at transsolar.com>
>>> >> To: "julia.feste" <julia.feste at whitepavilion.com.cn>
>>> >> Date: Wed, 3 Nov 2010 11:37:08 +0100
>>> >> Subject: Re: [TRNSYS-users] google sketchup+trnsys3d
>>> >> Hi,
>>> >>
>>> >> that's a well known problem that will be fixed in the next version.
>>> >> Hopefully upcoming within the next weeks.
>>> >>
>>> >> Regards
>>> >> Christian
>>> >>
>>> >> TRANSSOLAR Software Team
>>> >> hotline at transsolar.com
>>> >>
>>> >> www.trnsys.de
>>> >> Transsolar KlimaEngineering - Technologien für energieeffizientes
>>> Bauen
>>> >> und Nutzerkomfort in Gebäuden
>>> >> Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart /
>>> >> Amtsgericht Stuttgart - HRB 23347 / USt-IdNr.: 99073/00911
>>> >> Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
>>> >> Dipl.Phys. Stefan Holst, Prof. Volkmar Bleicher
>>> >>
>>> >> -----Ursprüngliche Nachricht-----
>>> >> Von: julia.feste [mailto:julia.feste at whitepavilion.com.cn]
>>> >> Gesendet: Mittwoch, 3. November 2010 06:46
>>> >> An: trnsys-users at cae.wisc.edu
>>> >> Betreff: [TRNSYS-users] google sketchup+trnsys3d
>>> >>
>>> >>
>>> >> Hello everybody,
>>> >> Thanks for your posts that's always really interesting!
>>> >> I come up with a problem using Google Sketchup and TRNSYS3D: inside a
>>> >> TRNSYS zone, I draft a square, then I want to pull it up at a certain
>>> >> height, so I write the number then Enter, and this error appears:
>>> >>
>>> >> <-----Beginning of the error----->
>>> >> ERROR:
>>> >> NoMethodError
>>> >> undefined method `position' for
>>> >> #<Sketchup::AttributeDictionary:0xfcb4eb8>
>>> >>
>>> >> BACKTRACE:
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `polygon_loop'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `each'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:309:in `polygon_loop'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:321:in `outer_polygon'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/sketchup/Sketchup.rb:326:in `polygon'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:27:in
>>> >> `detect_base_face'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in `each'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/DrawingUtils.rb:20:in
>>> >> `detect_base_face'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:254:in `face_polygon'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in `each'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:253:in `face_polygon'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/Surface.rb:107:in
>>> >> `update_input_object'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/BaseSurface.rb:94:in
>>> >> `update_input_object'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/interfaces/DrawingInterface.rb:353:in
>>> >> `on_change_entity'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/observers/FaceObserver.rb:32:in
>>> `onChangeEntity'
>>> >> C:/Program Files/Google/Google SketchUp
>>> >> 8/Plugins/Trnsys3d/lib/AsynchProc.rb:17:in `initialize'
>>> >>
>>> >> <-----End of the error----->
>>> >>
>>> >> When I pull it up manual, I don't have any problem, just when I write
>>> >> the number.
>>> >>
>>> >> Thanks in advance for your help,
>>> >> Julia.
>>> >> ________________________________________
>>> >> From: trnsys-users-request at cae.wisc.edu
>>> >> [trnsys-users-request at cae.wisc.edu]
>>> >> Sent: Wednesday, November 03, 2010 1:04 AM
>>> >> To: trnsys-users at cae.wisc.edu
>>> >> Subject: TRNSYS-users Digest, Vol 71, Issue 4
>>> >>
>>> >> Send TRNSYS-users mailing list submissions to
>>> >> trnsys-users at cae.wisc.edu
>>> >>
>>> >> To subscribe or unsubscribe via the World Wide Web, visit
>>> >> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >> or, via email, send a message with subject or body 'help' to
>>> >> trnsys-users-request at cae.wisc.edu
>>> >>
>>> >> You can reach the person managing the list at
>>> >> trnsys-users-owner at cae.wisc.edu
>>> >>
>>> >> When replying, please edit your Subject line so it is more specific
>>> than
>>> >> "Re: Contents of TRNSYS-users digest..."
>>> >>
>>> >> _______________________________________________
>>> >> TRNSYS-users mailing list
>>> >> TRNSYS-users at cae.wisc.edu
>>> >> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> ---------- 已转发邮件 ----------
>>> >> From: "Emiliano Casati - 3ME" <E.I.M.Casati at tudelft.nl>
>>> >> To: <trnsys-users at cae.wisc.edu>
>>> >> Date: Wed, 3 Nov 2010 13:19:58 +0100
>>> >> Subject: [TRNSYS-users] input file
>>> >>
>>> >> Hi to everybody!
>>> >>
>>> >> I don’t understand why, for certain projects, I can’t open the input
>>> >> file,
>>> >> the message is “the system cannot find the path specified”.
>>> >>
>>> >> Where should I find the input file?
>>> >>
>>> >>
>>> >>
>>> >> Thanks a lot
>>> >>
>>> >>
>>> >>
>>> >> ec
>>> >>
>>> >>
>>> >> ---------- 已转发邮件 ----------
>>> >> From: "Timothy McDowell" <mcdowell at tess-inc.com>
>>> >> To: "Thibaut VITTE" <thibaut.vitte at h3c-energies.fr>,
>>> >> trnsys-users at cae.wisc.edu
>>> >> Date: Wed, 3 Nov 2010 07:23:05 -0500 (CDT)
>>> >> Subject: Re: [TRNSYS-users] GenOpt optimization: problem for the
>>> >> secondgeneration after 5 simulations
>>> >> This type of error in GenOpt is usually caused by an error in the
>>> TRNSYS
>>> >> simulation. You need to check the *.lst file for the TRNSYS run to
>>> see
>>> >> what the TRNSYS error is.
>>> >>
>>> >> Regards,
>>> >>
>>> >> Tim
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> ----------------------------------
>>> >> Timothy McDowell
>>> >> Executive Vice President
>>> >> Thermal Energy System Specialists, LLC
>>> >> 22 N. Carroll St, Suite 370
>>> >> Madison, WI 53703
>>> >> Phone: 608-274-2577
>>> >> Fax: 608-278-1475
>>> >>
>>> >> ----- Original Message -----
>>> >> From: "Thibaut VITTE" <thibaut.vitte at h3c-energies.fr>
>>> >> Sent: Wed, November 3, 2010 5:27
>>> >> Subject:Re: [TRNSYS-users] GenOpt optimization: problem for the
>>> >> secondgeneration after 5 simulations
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> Dear Alexis,
>>> >>
>>> >> I've had a similar error when I used Genopt. I've had several
>>> >> components tracked by a "trace" command that made my list file
>>> >> enormous (more than 100Mb) and genopt could'nt handle that amount
>>> of
>>> >> data.
>>> >>
>>> >> Just my 2cents.
>>> >>
>>> >> Thibaut
>>> >> --
>>> >>
>>> >>
>>> >> .bodyclass @page { size: 8.5in 11in; margin-top: 0.7874in;
>>> >> margin-bottom:
>>> >> 0.7874in; margin-left: 0.7874in; margin-right: 0.7874in }
>>> >> .bodyclass table { border-collapse:collapse; border-spacing:0;
>>> >> empty-cells:show }
>>> >> .bodyclass td, th { vertical-align:top; font-size:12pt;}
>>> >> .bodyclass h1, h2, h3, h4, h5, h6 { clear:both }
>>> >> .bodyclass ol, ul { margin:0; padding:0;}
>>> >> .bodyclass li { list-style: none; margin:0; padding:0;}
>>> >> .bodyclass li span.odfLiEnd { clear: both; line-height:0;
>>> width:0;
>>> >> height:0; margin:0; padding:0; }
>>> >> .bodyclass span.footnodeNumber { padding-right:1em; }
>>> >> .bodyclass * { margin:0; }
>>> >> .bodyclass .fr1 { font-size:12pt; text-align:center;
>>> >> vertical-align:top;
>>> >> margin-left:0in; margin-right:0in; margin-top:0in; margin-bottom:0in;
>>> >> padding:0in; border-style:none; }
>>> >> .bodyclass .P1 { font-size:12pt; margin-bottom:0in;
>>> margin-top:0in;
>>> >> font-family:Times New Roman; text-align:center ! important; }
>>> >> .bodyclass .P10 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify ! important;
>>> >> color:#f79646; }
>>> >> .bodyclass .P2 { font-size:9pt; margin-bottom:0in;
>>> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:center ! important;
>>> >> color:#e36c0a; font-style:italic; font-weight:bold; }
>>> >> .bodyclass .P3 { font-size:9pt; margin-bottom:0in;
>>> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify ! important;
>>> >> color:#e36c0a; font-weight:bold; }
>>> >> .bodyclass .P4 { font-size:9pt; margin-bottom:0in;
>>> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify ! important;
>>> >> color:#e36c0a; font-weight:bold; }
>>> >> .bodyclass .P5 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; color:#e36c0a; font-weight:bold; }
>>> >> .bodyclass .P6 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify ! important;
>>> >> color:#3329b1; }
>>> >> .bodyclass .P61 { font-size:8.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify ! important;
>>> >> color:#3329b1; }
>>> >> .bodyclass .P7 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify ! important;
>>> >> color:#3329b1; font-style:italic; }
>>> >> .bodyclass .P8 { font-size:7.5pt; margin-bottom:0in;
>>> >> margin-top:0in;
>>> >> font-family:Tahoma, sans-serif; text-align:justify ! important;
>>> >> color:#3329b1; font-style:italic; }
>>> >> .bodyclass .P9 { font-size:12pt; margin-bottom:0in;
>>> margin-top:0in;
>>> >> font-family:Times New Roman; text-align:justify ! important; }
>>> >> .bodyclass .P91 { font-size:12pt; margin-bottom:0in;
>>> >> margin-top:0.05in;
>>> >> font-family:Times New Roman; text-align:justify ! important; }
>>> >> .bodyclass .Standard { font-size:12pt; font-family:Times New
>>> Roman;
>>> >> }
>>> >> .bodyclass .T1 { color:#f79646; }
>>> >> .bodyclass .T2 { color:#f79646; font-family:Tahoma, sans-serif;
>>> >> font-size:7.5pt; }
>>> >> .bodyclass .T3 { color:#3329b1; font-family:Tahoma, sans-serif;
>>> >> font-size:7.5pt; }
>>> >> .bodyclass { }
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> Le futur maîtrisé
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> Thibaut VITTE
>>> >> Docteur - Ingénieur Energies
>>> >> Mail : thibaut.vitte at h3c-energies.fr
>>> >>
>>> >> -----------------------------
>>> >> H3C-énergies
>>> >> 35, chemin du vieux Chêne - 38240 MEYLAN
>>> >> Tél : 04 76 41 88 66 – Fax : 04 76 41 28
>>> >> 94
>>> >> www.h3c-energies.fr
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> -----------------------------------------------------------------------------------
>>> >> Afin de contribuer au respect de l'environnement,
>>> >> merci de n'imprimer ce message qu'en cas de nécessité.
>>> >> In order to respect the environment, please don't
>>> >> print this e-mail unless you really need to.
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >>
>>> >> _______________________________________________
>>> >> TRNSYS-users mailing list
>>> >> TRNSYS-users at cae.wisc.edu
>>> >> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >>
>>> >>
>>> >> ----- End of original message -----
>>> >>
>>> >>
>>> >>
>>> >> _______________________________________________
>>> >> TRNSYS-users mailing list
>>> >> TRNSYS-users at cae.wisc.edu
>>> >> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >>
>>> >>
>>> >
>>> > _______________________________________________
>>> > TRNSYS-users mailing
>>>
>>> > listTRNSYS-users at cae.wisc.eduhttps://
>>> www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>> >
>>> >
>>> > --
>>> > ***************************
>>> > David BRADLEY
>>> > Principal
>>> > Thermal Energy Systems Specialists, LLC
>>> > 22 North Carroll Street - suite 370
>>> > Madison, WI 53703 USA
>>> >
>>> > P:+1.608.274.2577
>>> > F:+1.608.278.1475d.bradley at tess-inc.com
>>> > http://www.tess-inc.comhttp:// <http://www.tess-inc.comhttp//>
>>> www.trnsys.com
>>> >
>>>
>>>
>>>
>>>
>>> --
>>> ***************************
>>> David BRADLEY
>>> Principal
>>> Thermal Energy Systems Specialists, LLC
>>> 22 North Carroll Street - suite 370
>>> Madison, WI 53703 USA
>>>
>>> P:+1.608.274.2577
>>> F:+1.608.278.1475
>>> d.bradley at tess-inc.com
>>> http://www.tess-inc.comhttp://www.trnsys.com
>>>
>>>
>>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475d.bradley at tess-inc.com
> http://www.tess-inc.comhttp://www.trnsys.com
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110705/842d977e/attachment-0001.htm>
More information about the TRNSYS-users
mailing list