Paris,

  You are on the right track. There are a number of other heat pump 
models available in the TESS HVAC library; like Type143 they too will 
give you COP as a function of entering conditions. They differ from 
Type143 in that the Type143 external performance data file is for a 
specific heat pump capacity while the heat pumps in the TESS library 
have normalized performance data files and the heat pump capacity is 
entered as parameters to the model.

kind regards,

  David


On 03/10/2022 08:49, Paris Pasqualin via TRNSYS-users wrote:
>
> Hello everyone,
>
> I understand that the cooling and heating energy demands generated by 
> Type56 are thermal energy. If I use a heat pump, that has a certain 
> COP, to provide the cooling and heating energy, does this mean the 
> electric energy requirement of the heat pump is (cooling + heating 
> energy)/COP? Can type 143 be used to calculate how the COP change? Is 
> there any other type that I can use to calculate the COP?
>
> Best regards,
>
> Paris
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220310/f3a0f405/attachment.htm>


More information about the TRNSYS-users mailing list