    <p> You are on the right track. There are a number of other heat
      pump models available in the TESS HVAC library; like Type143 they
      too will give you COP as a function of entering conditions. They
      differ from Type143 in that the Type143 external performance data
      file is for a specific heat pump capacity while the heat pumps in
      the TESS library have normalized performance data files and the
      heat pump capacity is entered as parameters to the model.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 03/10/2022 08:49, Paris Pasqualin
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:04a011c4c60e4dda89793c28a1cf62df@student.bham.ac.uk">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:"Yu Gothic";
        panose-1:2 11 4 0 0 0 0 0 0 0;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}@font-face
        {font-family:"\@Yu Gothic";
        panose-1:2 11 4 0 0 0 0 0 0 0;}@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}span.EmailStyle21
        {mso-style-type:personal-reply;
        font-family:"Calibri",sans-serif;
        color:windowtext;}.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}div.WordSection1
        {page:WordSection1;}</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">Hello everyone,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">I understand that the cooling and heating
          energy demands generated by Type56 are thermal energy. If I
          use a heat pump, that has a certain COP, to provide the
          cooling and heating energy, does this mean the electric energy
          requirement of the heat pump is (cooling + heating
          energy)/COP? Can type 143 be used to calculate how the COP
          change? Is there any other type that I can use to calculate
          the COP?<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Best regards,<o:p></o:p></p>
        <p class="MsoNormal">Paris<o:p></o:p></p>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>