[TRNSYS-users] Multiple zones on same mechanical components

David BRADLEY d.bradley at tess-inc.com
Mon May 24 09:00:39 PDT 2021


Just as in real life a thermostat cannot get information from more than 
one sensor so too the TRNSYS thermostat model can only monitor one 
temperature (although it shouldn't crash if you try to connect more than 
one; we'll look into that). You need to decide in which Type56 zone your 
thermostat is going to be located. The temperature control in the other 
parts of the building isn't going to be as good but again, that is how a 
building works in reality. You can of course feed the Type56 zone 
temperatures through an equation or a component that takes the average 
temperature of the Type56 zones and then allow your thermostat to 
monitor the average temperature rather than a specific temperature.

kind regards,

  David


On 05/24/2021 07:30, Misbaudeen Adesanya via TRNSYS-users wrote:
> Dear TRNSYS users,
> I am modelling the performance of an air to water heat pump (Type 941) 
> used for heating a greenhouse (Type 56) that consists of three zones. 
> Each of the zones housed different crops and the temperature is to be 
> conditioned by a thermostat (Type 166)  using temperature level 
> control mechanism. Anytime I connect multiple output (zone 
> temperatures) from Type 56 to the same input in Type 166 (monitoring 
> temperature), TRNSYS will shut down by itself.
>
> Please how do I solve this problem or is there any other alternative?
>
> Thank you.
>
> -- 
> Adesanya Misbaudeen Aderemi
> Department of Agricultural Civil Engineering
> College of Agricultural & Life Sciences
> Kyungpook National University
> 1370 Sangyuk-dong, Puk-gu
> Daegu 702-701, South Korea
> 대구시 북구 산격동 경북대학교 농업토목공학과
> Cell phone: +82-10-5168-7503
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210524/1e5704a0/attachment.htm>


More information about the TRNSYS-users mailing list