[TRNSYS-users] HELP with TRNSYS3D
David BRADLEY
d.bradley at tess-inc.com
Wed Jan 13 07:05:45 PST 2021
Toni,
I think the problem with your file is that the basement ceiling is a
single surface that does not correspond to (ie is not the same size and
shape as) the floors of the zones above. Like we did with the other
case, you have to draw lines on the basement ceiling that correspond to
each of the floor plates of the zones above. Since you have 14 zones
that make up the floor above, your basement ceiling needs to be cut into
14 pieces.
kind regards,
David
On 01/13/2021 06:02, Toni Calabrese via TRNSYS-users wrote:
>
> Hi everyone,
>
> I have a huge problem and I do not know if it is a problem in Trnsys3D
> or TRNBUILD. Attached you can find the IDF file. I drawn a complete
> flat (Ground Floor) and below it I drawn the cellar as a single zone
> connected to the ground floor.
>
> Could you firstly check if all the walls (in particular ADJ Walls
> between the rooms of the ground floor and the ceiling between ground
> floor and cellar) are defined correctly?
>
> I tried to import this model in Trnsys via 3d Wizard but it is not
> able to import the model (it is always loading the file) and I do not
> know why.
>
> Could you maybe try to import it in trnsys and see if in your case it
> works?
>
> Thanks a lot and have a nice day.
>
> ------------------------------------------------------------------------
>
> *Toni Calabrese*, MSc.
>
> Wissenschaftlicher Projektmitarbeiter
>
> toni.calabrese at spf.ch <mailto:toni.calabrese at spf.ch>
> |toni.calabrese at ost.ch <mailto:toni.calabrese at ost.ch>
>
> T +41 58 257 4827
>
> SPF Institut für Solartechnik
>
> OST – Ostschweizer Fachhochschule
>
> Oberseestr. 10 | CH-8640 Rapperswil | Switzerland | _www.spf.ch
> <http://www.spf.ch>_| _www.ost.ch <http://www.ost.ch>_
>
> OST – Ostschweizer Fachhochschule ist der Zusammenschluss aus FHS
> St.Gallen, HSR Rapperswil und NTB Buchs.
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210113/04201c0d/attachment.htm>
More information about the TRNSYS-users
mailing list