[TRNSYS-users] problem with type 11b
David BRADLEY
d.bradley at tess-inc.com
Fri Dec 18 06:33:49 PST 2020
Are you dividing your flow by a simple fraction (80% goes to the boiler
and 20% goes to recirculation for example) or is the Type11 set up so
that it tries to maintain a set point temperature like a tempering valve
might do? The error that you are getting is one that comes when Type11
is used as a tempering valve but can't achieve the set point because
both of the inlet temperatures are already above the set point. A little
additional explanation might help me find a suggestion for how to work
around the issue.
kind regards,
David
On 12/18/2020 08:02, Filippo Angeli via TRNSYS-users wrote:
> Good morning,
> simulating the operation of a condensing boiler with a power of 20kW
> and a setpoint temperature of 50 degrees; I get the following error,
> which I report later, in type 11b. With this type I divide my flow
> rate into the boiler flow rate and the recirculation flow rate.
> "The inlet temperature and the heat source temperature have
> simultaneously exceeded the set point temperature. Gamma has been set
> to 0 (Mode 4) or 1 (Mode 5)."
> I would like to have your help. Thanks.
>
> Angeli Filippo
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20201218/a13a18fd/attachment.html>
More information about the TRNSYS-users
mailing list