<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body>
    <p>Are you dividing your flow by a simple fraction (80% goes to the
      boiler and 20% goes to recirculation for example) or is the Type11
      set up so that it tries to maintain a set point temperature like a
      tempering valve might do? The error that you are getting is one
      that comes when Type11 is used as a tempering valve but can't
      achieve the set point because both of the inlet temperatures are
      already above the set point. A little additional explanation might
      help me find a suggestion for how to work around the issue.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 12/18/2020 08:02, Filippo Angeli via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:1618744424.3439293.1608300129039@mail.yahoo.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div class="yahoo-style-wrap" style="font-family:Helvetica Neue,
        Helvetica, Arial, sans-serif;font-size:13px;">
        <div dir="ltr" data-setdir="false">
          <div>
            <div dir="ltr" data-setdir="false">Good morning,</div>
            <div>simulating the operation of a condensing boiler with a
              power of 20kW and a setpoint temperature of 50 degrees; I
              get the following error, which I report later, in type
              11b. With this type I divide my flow rate into the boiler
              flow rate and the recirculation flow rate.</div>
            <div>"The inlet temperature and the heat source temperature
              have simultaneously exceeded the set point temperature.
              Gamma has been set to 0 (Mode 4) or 1 (Mode 5)."</div>
            <div>I would like to have your help. Thanks.</div>
            <div><br>
            </div>
            <div dir="ltr" data-setdir="false">Angeli Filippo</div>
          </div>
          <br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>