[TRNSYS-users] Using which component?
David BRADLEY
d.bradley at tess-inc.com
Wed Sep 25 12:19:41 PDT 2019
Vajhie,
You should use Type2. Almost all of the examples that involve solar
water heating systems use Type2; I would suggest that you look at one of
them to understand how to implement Type2.
kind regards,
David
On 09/25/2019 13:56, Vajihe Davoodi via TRNSYS-users wrote:
> Hi,
> I have a solar heating simulation.I have a storage thank in it. I want
> to say that whenever the inlet temperature of the tank (outlet
> collector temperature) is less than outlet temperature of the tank
> (inlet collector temperature), turn off the pump. From which component
> I should use? And how?
>
> Regards
>
> Vajihe
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************