[TRNSYS-users] Issue in auxiliary operations with Type941 (Heat Pump from TESS)

LECONTE Antoine 219492 Antoine.LECONTE at cea.fr
Mon Oct 28 02:59:06 PDT 2019


I have noticed a potential issue with the use of the auxiliary system of the Heat Pump Type 941 (from TESS library).

In the source code (Type941.for), there is no value setting for QAUX when all signals à "OFF".
This means that an auxiliary consumption can be computed whereas its operation mode is "OFF".
For instance : in one time step you have "Heating mode " and "Aux mode" both "ON"; if in the next timestep all signals are "OFF", Type 941 will still set QAUX > 0 as an output.
This can be easily fixed by either adding an additional condition on the calculation of QAUX directly in the TRNSYS model or by re-compiling type 941 with an additional "QAUX=0." In the "NO-FLOW CONDITIONS".

Best regards,

------------------------------------------------------------------------------------------
[Description : cid:image001.png at 01CF110C.81BE0EF0]

Antoine LECONTE
Research Engineer
National Institute of Solar Energy
CEA/LITEN - Department of Solar Energy
Building and Thermal Systems

Commissariat à l'énergie atomique et aux énergies alternatives
Bât. HELIOS, 50 avenue du Lac Léman | F-73375 Le Bourget-du-Lac
T. +33 (0)4 79 79 21 38 | F. +33 (0) 4 79 62 13 74 |
antoine.leconte at cea.fr<mailto:antoine.leconte at cea.fr>; www.ines-solaire.org<http://www.ines-solaire.org/>; liten.cea.fr

------------------------------------------------------------------------------------------

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191028/46de4df3/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 10820 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191028/46de4df3/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1321 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191028/46de4df3/attachment-0001.jpg>


More information about the TRNSYS-users mailing list