There is no representation of shading surfaces visible in TRNBuild.
In order to see the impact of shading, you'll need to generate the
shading matrix file from TRNBuild, which is an option in the TRNBuild
Tools menu. This will create a file with the extension *.shm. If the
*.shm file is found in the same location as the *.b18 file then shading
will be taken into account. If you move the *.shm file then shading will
be ignored. Also keep in mind that Type56 assesses the impact of shading
only on windows, not on walls so if your building has very few windows
then the impacts may be minimal.
kind regards,
David
On 12/30/2019 11:47, Fernanda Sánchez via TRNSYS-users wrote:
>
> Hi Everyone,
>
> I have a problem with the shading zones in my model. I draw two
> shading groups and 3 thermal zones in trnsys 3D (Sketschup). When I
> import the idf file in trnbuild, fist I can’t see the shading zones, I
> see only the thermal zones. Then when I simulate the operative
> temperature of the thermal zones that have shading, I got the same
> results as when I simulate the same thermal zones without shading. So
> I can´t see any different with shading and without shading. I already
> use the tool generate shading/isolation matrix but I can´t see any
> different.
>
> Can anyone help me with that? I could be grateful
>
> Best regards and happy New Year
>
> Fernanda
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191231/6f24ce79/attachment-0001.html>
More information about the TRNSYS-users
mailing list