Al-Hyari,
It is not really possible to know what might be going wrong without
running the project. What I would suggest is that you make a new project
to which you add only the exhaust and outdoor air fans. Make sure they
are the right size by adjusting parameter values and run the simulation
using an online plotter to verify that the temperature, humidity and
flow rate leaving the fans is as you planned for it to be. Next, add the
heat wheel into the system. Again, make sure that the parameters are
correctly set so that the heat wheel is appropriately sized to the
application. Again, use the online plotter to verify that the
temperatures, humidities, and flow rates exiting the wheel make sense.
Keep adding one component at a time and verifying as you go.
kind regards,
David
On 11/06/2018 05:44, Al-hyari via TRNSYS-users wrote:
> Dear Everyone
>
> so i tried by my own to build the model for an AHU Equipped with a
> heat wheel and auxiliary dx coil connected to a VRV System
>
> i want to know the values of temperature and relative humidity before
> and after the heat wheel. but there is some mistake that i can not
> figure it out.
>
> please advise me what can i do to make the correct model to simulate
>
> in the attached files you can find the trnsys model and the schematic
> diagram for the AHU
>
>
> Regards
>
>
>
>
>
>
>
> On Tuesday, October 30, 2018, 3:30:38 PM GMT+1, Al-hyari via
> TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
>
>
> Dear Colleagues
>
> It is my pleasure to join this discussing group mail.
>
> so my question is :
>
> I am working to simulate an AHU equipped with Heat wheel and an
> auxiliary dx coil connected to a VRV system.
>
> I am new on TrnSys and i don't have much knowledge.
>
> So if any one could help me by sendeng a similar example to study on
> it and make modification on the block diagram i would be highly
> appreciated.
>
> Regards
> Laith F. Al-Hyari
>
>
> _______________________________________________
> TRNSYS-users mailing list
>
> TRNSYS-users at lists.onebuilding.org
> <mailto:TRNSYS-users at lists.onebuilding.org>
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181107/83355a54/attachment.html>
More information about the TRNSYS-users
mailing list