[TRNSYS-users] Antiproportional behaviour of PID

Daniel Uhl d at f26.at
Thu Feb 1 03:51:27 PST 2018


Have you tried just using a negative number for the proportional value of your controller?

Yours,
Daniel

Am 01.02.2018 um 12:21 schrieb s0537085 via TRNSYS-users:
> Hi,
>
> I´m trying to set PID-controller to following:
>
> If temperature is too high, a flow rate should increase, as well.
>
> If temperature is too low, flow rate should decrease.
>
> So far, PID- controllers usually do right the other way round: If
> temperature too low, increase flow rate.
>
> In my system, I want to heat an air flow in a cross flow heat exchanger.
> If the air flow rate is too high, it exceeds the heat exchangers power,
> and the outlet temperature can´t reach the desired temperature.
>
> Thanks
>
> Tom
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>



More information about the TRNSYS-users mailing list