[TRNSYS-users] Type 16 (radiation processor)
David BRADLEY via TRNSYS-users
trnsys-users at lists.onebuilding.org
Mon Sep 12 07:34:35 PDT 2016
Adnan,
The default mode for Type56 in Trnsys17 is to get its radiation
automatically from the weather data file that provides the ambient
temperature to the model. If you do not want to use this default mode,
however, you do not have to. In order to change to the manual mode:
1. open the building project in TRNBuild and activate the "project"
window. You'll see a list of orientations, each of which has a
calculation mode that is set to "internal"
2. double click on an orientation for which you do not want the
calculation mode to be internal. In the case of using Type16, you'll
need to do this with all the orientations.
3. in the window that pops up change the radio button from "internal" to
"external by another component"
4. once you have changed all the orientations to "external by another
component" save the building project, return to the Simulation Studio,
right click on the Type56 icon and select "update building variable list"
kind regards,
David
On 09/11/2016 04:43, adnan rasheed via TRNSYS-users wrote:
> Thank you very much Jaff for answering me. To solve a little more
> confusion, i need your kind attention. As I want to apply radiation
> data on my
>
> building by connecting TYPE 16 with TYPE 56 and gives there all the
> surface orientations. In a TYPE 56 there is no input to connect with
> solar
>
> radiation. If I add new inputs on the basis of my orientations and
> then attached all radiation output of TYPE 16 as an input in TYPE 56
> does it will
>
> work? and give me the total solar energy gain inside???
>
> Regards
> Adnan
>
> On Sun, Sep 11, 2016 at 3:18 AM, Jeff Thornton <thornton at tess-inc.com
> <mailto:thornton at tess-inc.com>> wrote:
>
> Use more than one Type 16 hooked up to the single Type 9.
>
> Jeff Thornton
> TESS
>
> Sent from my iPhone
>
> > On Sep 10, 2016, at 6:55 AM, adnan rasheed via TRNSYS-users
> <trnsys-users at lists.onebuilding.org
> <mailto:trnsys-users at lists.onebuilding.org>> wrote:
> >
> > Hello everyone,
> >
> > My question is about TRNSYS type 9 (weather data reader) and
> type 16 (radiation processor). I am using feild weather data to
> apply to a building 3d model by using type 56. I have 17 surfaces
> (beacause of my roof design) in the model and type 16 only allows
> 8 surfaces to give output for,
> >
> > when i connect 3d model with type 15 (weather data reader and
> processor) it automatically connect 17 surfaces. But I cannot use
> type 15 because I need to use my own weather data in text file.
> How can I deal with that.
> >
> >
> >
> > Best regards
> >
> > Adnan
> > PhD student
> > _______________________________________________
> > TRNSYS-users mailing list
> > TRNSYS-users at lists.onebuilding.org
> <mailto:TRNSYS-users at lists.onebuilding.org>
> >
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
> <http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com