<p>Adnan,</p>
<p> The default mode for Type56 in Trnsys17 is to get its radiation
automatically from the weather data file that provides the ambient
temperature to the model. If you do not want to use this default
mode, however, you do not have to. In order to change to the
manual mode:</p>
<p>1. open the building project in TRNBuild and activate the
"project" window. You'll see a list of orientations, each of which
has a calculation mode that is set to "internal"</p>
<p>2. double click on an orientation for which you do not want the
calculation mode to be internal. In the case of using Type16,
you'll need to do this with all the orientations.</p>
<p>3. in the window that pops up change the radio button from
"internal" to "external by another component"</p>
<p>4. once you have changed all the orientations to "external by
another component" save the building project, return to the
Simulation Studio, right click on the Type56 icon and select
"update building variable list"<br>
</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<p><br>
</p>
<br>
<div class="moz-cite-prefix">On 09/11/2016 04:43, adnan rasheed via
TRNSYS-users wrote:<br>
</div>
<blockquote
cite="mid:CAG9tXZjqB-SttNkChux9sME+EOoAHEdDtVH=ArDKyM8kAO2T_Q@mail.gmail.com"
type="cite">
<div dir="ltr">Thank you very much Jaff for answering me. To solve
a little more confusion, i need your kind attention. As I want
to apply radiation data on my
<div><br>
</div>
<div> building by connecting TYPE 16 with TYPE 56 and gives
there all the surface orientations. In a TYPE 56 there is no
input to connect with solar </div>
<div><br>
</div>
<div>radiation. If I add new inputs on the basis of my
orientations and then attached all radiation output of TYPE 16
as an input in TYPE 56 does it will </div>
<div><br>
</div>
<div>work? and give me the total solar energy gain inside??? </div>
<div><br>
</div>
<div>Regards</div>
<div>Adnan </div>
</div>
<div class="gmail_extra"><br>
<div class="gmail_quote">On Sun, Sep 11, 2016 at 3:18 AM, Jeff
Thornton <span dir="ltr"><<a moz-do-not-send="true"
href="mailto:thornton@tess-inc.com" target="_blank">thornton@tess-inc.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0
.8ex;border-left:1px #ccc solid;padding-left:1ex">Use more
than one Type 16 hooked up to the single Type 9.<br>
<br>
Jeff Thornton<br>
TESS<br>
<br>
Sent from my iPhone<br>
<div>
<div class="h5"><br>
> On Sep 10, 2016, at 6:55 AM, adnan rasheed via
TRNSYS-users <<a moz-do-not-send="true"
href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.<wbr>onebuilding.org</a>>
wrote:<br>
><br>
> Hello everyone,<br>
><br>
> My question is about TRNSYS type 9 (weather data
reader) and type 16 (radiation processor). I am using
feild weather data to apply to a building 3d model by
using type 56. I have 17 surfaces (beacause of my roof
design) in the model and type 16 only allows 8 surfaces
to give output for,<br>
><br>
> when i connect 3d model with type 15 (weather data
reader and processor) it automatically connect 17
surfaces. But I cannot use type 15 because I need to use
my own weather data in text file. How can I deal with
that.<br>
><br>
><br>
><br>
> Best regards<br>
><br>
> Adnan<br>
> PhD student<br>
</div>
</div>
> ______________________________<wbr>_________________<br>
> TRNSYS-users mailing list<br>
> <a moz-do-not-send="true"
href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.<wbr>onebuilding.org</a><br>
> <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
rel="noreferrer" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
<br>
</blockquote>
</div>
<br>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>