Both of those components base their estimate of performance on a
performance map that gives (essentially) device capacity and COP as a
function of the current inlet conditions. The refrigerant and indeed all
the inner workings of the device are irrelevant because their properties
are built in to the performance map. It is recommended that you find a
performance map for the specific equipment that you are trying to model
if at all possible. Such data can often be obtained from manufacturers
in their published literature.
kind regards,
David
On 10/22/2015 09:58, wajahat Khan wrote:
> My question is regarding Adsorption chiller type 909 and absorption
> chiller type 107.
>
> Both of these chillers have external files for different parameters
> but there is no information about the refrigerant absorbent pair in
> case of absorption chiller ie which refrigerant absorbent pair is
> used.Similarly i didnt find any information about refrigerant
> adsorbent pair used in adsorption chiller.No information available
> that data available in external files is for which pair?
> Any have idea about this?
>
> --
> *Engr M Wajahat Khan
> *
> *MS Mechanical
> *
> *Cryogenic Engineer*
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20151023/34970204/attachment-0002.htm>
More information about the TRNSYS-users
mailing list