Wu,
Type666 models a chiller that can modulate its capacity using
internal controls to maintain a steady chilled water outlet temperature.
I would think that using the chiller on/off signal would result in the
outlet chilled water temperature either being equal to the inlet
temperature or being equal to the user-defined chilled water setpoint
temperature so long as the chiller has enough capacity to meet the
setpoint. Usually when I have seen staged chillers in a project each
chiller is able to modulate its capacity internally and multiple
chillers are staged sequentially as they reach their respective
capacities. I have not run across a chiller that did not have the
ability to run at part load so as to maintain a setpoint. If you are
looking for a model of a chiller stack that contains multiple variable
capacity chillers then I have written such a component. In order to use
it you would need to define equations or use a controller component that
would decide how many of the chillers should be on at any given time. If
you are interested in purchasing the component, please contact me
directly and I can estimate the cost.
kind regards,
David
On 10/28/2015 00:12, 吴伟伟v v wrote:
>
> Dear users,
>
> Hi all!
>
> I’m using TRNSYS to model a typical HVAC system,i.e.,chiller( type666)
> and fan coil(type 508a) combined a building model(type 56). I set a
> room thermostat(type645) for room temperature control, but I found
> that the chiller has oscillations which result in chilled water
> temperature fluctuated strongly several times even in an hour。My
> question is as following:
>
> 1.Is there any idea to control Type666 to output its cooling capacity
> as 0.25,0.5,0.75, 1,like stages control?
>
> 2.Should I set more chiller(equally sized) in the model to realize the
> number of chillers control instead of one chiller?
>
> I did not found the relevant information in the forum. Can someone
> please help me with this issue?
>
> With best wishes
>
> Yours sincerely
>
> Wu weiwei
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20151028/c080cbd3/attachment-0001.htm>
More information about the TRNSYS-users
mailing list