<html>
  <head>
    <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Wu,<br>
      Type666 models a chiller that can modulate its capacity using
    internal controls to maintain a steady chilled water outlet
    temperature. I would think that using the chiller on/off signal
    would result in the outlet chilled water temperature either being
    equal to the inlet temperature or being equal to the user-defined
    chilled water setpoint temperature so long as the chiller has enough
    capacity to meet the setpoint. Usually when I have seen staged
    chillers in a project each chiller is able to modulate its capacity
    internally and multiple chillers are staged sequentially as they
    reach their respective capacities. I have not run across a chiller
    that did not have the ability to run at part load so as to maintain
    a setpoint. If you are looking for a model of a chiller stack that
    contains multiple variable capacity chillers then I have written
    such a component. In order to use it you would need to define
    equations or use a controller component that would decide how many
    of the chillers should be on at any given time. If you are
    interested in purchasing the component, please contact me directly
    and I can estimate the cost.<br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/28/2015 00:12, 吴伟伟v v wrote:<br>
    </div>
    <blockquote cite="mid:BLU180-W50436CBE8A769BF56B904D2210@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 12pt;
font-family:微软雅黑
}
--></style>
      <div dir="ltr">
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">Dear users,
            <!--?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office" /--><o:p></o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US"><o:p> </o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">Hi all!<o:p></o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">I’m using TRNSYS to model a typical HVAC
            system,i.e.,chiller( type666) and fan coil(type 508a)
            combined a building model(type 56). I set a room
            thermostat(type645) for room temperature control, but I
            found that the chiller has oscillations which result in
            chilled water temperature fluctuated strongly <span
              style="mso-spacerun: yes"> </span>several times even in an
            hour</span><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt">。<span
              lang="EN-US">My question is as following:<o:p></o:p></span></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US"><o:p> </o:p></span></p>
        <p style="TEXT-ALIGN: left; TEXT-INDENT: -18pt; MARGIN: 0cm 0cm
          0pt 18pt; mso-pagination: widow-orphan; tab-stops: 45.8pt
          91.6pt 137.4pt 183.2pt 229.0pt 274.8pt 320.6pt 366.4pt 412.2pt
          458.0pt 503.8pt 549.6pt 595.4pt 641.2pt 687.0pt 732.8pt;
          mso-char-indent-count: 0; mso-list: l0 level1 lfo1"
          class="MsoListParagraph" align="left"><span
            style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US"><span style="mso-list: Ignore">1.<span
                style="FONT: 7pt 'Times New Roman'">  </span></span></span><span
            style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">Is there any idea to control Type666 to output
            its cooling capacity as 0.25,0.5,0.75, 1,like stages
            control? <o:p></o:p></span></p>
        <p style="TEXT-ALIGN: left; TEXT-INDENT: -18pt; MARGIN: 0cm 0cm
          0pt 18pt; mso-pagination: widow-orphan; tab-stops: 45.8pt
          91.6pt 137.4pt 183.2pt 229.0pt 274.8pt 320.6pt 366.4pt 412.2pt
          458.0pt 503.8pt 549.6pt 595.4pt 641.2pt 687.0pt 732.8pt;
          mso-char-indent-count: 0; mso-list: l0 level1 lfo1"
          class="MsoListParagraph" align="left"><span
            style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US"><span style="mso-list: Ignore">2.<span
                style="FONT: 7pt 'Times New Roman'">  </span></span></span><span
            style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">Should I set more chiller(equally sized) in the
            model to realize the number of chillers control instead of
            one chiller?</span><span style="FONT-FAMILY: 宋体; FONT-SIZE:
            12pt; mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US"><o:p> </o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US"><o:p> </o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">I did not found the relevant information in the
            forum. Can someone please help me with this issue?<o:p></o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US"><o:p> </o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">With best wishes<o:p></o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">Yours sincerely<o:p></o:p></span></p>
        <p style="TEXT-ALIGN: left; MARGIN: 0cm 0cm 0pt; mso-pagination:
          widow-orphan; tab-stops: 45.8pt 91.6pt 137.4pt 183.2pt 229.0pt
          274.8pt 320.6pt 366.4pt 412.2pt 458.0pt 503.8pt 549.6pt
          595.4pt 641.2pt 687.0pt 732.8pt" class="MsoNormal"
          align="left"><span style="FONT-FAMILY: 宋体; FONT-SIZE: 12pt;
            mso-bidi-font-family: 宋体; mso-font-kerning: 0pt"
            lang="EN-US">Wu weiwei<o:p></o:p></span></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>