[TRNSYS-users] Initializing wall temperature
David BRADLEY
d.bradley at tess-inc.com
Mon Oct 5 09:20:56 PDT 2015
Marcello,
To my knowledge there is not a way to precondition the walls. I would
expect that with such thick walls you would need to run the building for
at least a 6 month period (if not a 1 year period) in order to get rid
of all the initial value transients. If it makes you feel any better to
know that you are not alone in your misery of waiting for a slow
simulation, I often have models that run more slowly than 1 month per 40
minutes! Some ground coupling simulations run at near real-time!
kind regards,
David
On 10/05/2015 08:06, marcello.caciolo at cofelyaxima-gdfsuez.com wrote:
>
> Dear Trnsys users,
>
> I am currently working on a very massive building, with many zones and
> very with high thermal inertia (concrete wall from 60 to 120 cm of
> thickness). The model takes 40 minutes to calculate 1 month.
>
> I observe than after one month, final temperatures in zones are still
> very depending on initial temperatures. For this reason, I tried to
> adjust initial temperature to be nearer to expected final temperatures
> (in the order of 35-40°C).
>
> However, in the first part of the simulation, temperatures drop
> quickly to 25-30°C, depending on the zone. This is quite surprising,
> considering that there are no heat losses and there are heat gains.
> The only explication I found is that surface temperatures are not
> initialized to initial temperature of the zone, and thermal mass takes
> time to warm up.
>
> Do you know if there is a way to force surface temperatures to zone
> temperatures at the beginning of a simulation ?
>
> Thank you !
>
> Best regards,
>
> *Marcello Caciolo*
> Responsable Outils et Méthodes d'Analyse Energétique
>
> cid:image003.jpg at 01CD4E08.954D04D0
> *
> *Service Engagement Energétique - Direction Ingénierie Conception
> 15 rue Nina Simone
> CS 39601 - 44096 Nantes Cedex 1
> Tél.: +33 02 40 41 06 57
> marcello.caciolo at cofelyaxima-gdfsuez.com
> <mailto:prenom.nom at aximaseitha-gdfsuez.com>
>
> P*Pensez à l'environnement avant d'imprimer ce message*
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20151005/423684fb/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4267 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20151005/423684fb/attachment.jpeg>
More information about the TRNSYS-users
mailing list