[TRNSYS-users] Type 56 inputs

David BRADLEY d.bradley at tess-inc.com
Fri May 15 09:06:40 PDT 2015


Anton,
  You can define more than one VENTILATION type for your zone. In many 
HVAC systems (especially in humid climates) it is typical for the 
outdoor air to mix with return air before passing across the cooling 
coil in which case you would only define a single VENTILATION type in 
TRNBuild. When you define the VENTILATION type make the air temperature, 
RH, and flow rate into INPUTS (as opposed to scheduled values) and then 
those inputs will show up in the Simulation Studio along with all the 
other Type56 inputs.
regards,
  David


On 5/14/2015 2:57 PM, Anton Åhlund wrote:
> Hi!
>
> I want to have a scheduled ventilation of a type 56 zone with outside 
> air, while at the same time have inputs(Temp, Rel.hum. and air flow) 
> for a cooling coil in the same zone.
>
> Is this possible? If it is, how can I do it?
>
>
> Best regards,
> Anton Åhlund
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150515/9fe98e9d/attachment.htm>


More information about the TRNSYS-users mailing list