<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Anton,<br>
     You can define more than one VENTILATION type for your zone. In
    many HVAC systems (especially in humid climates) it is typical for
    the outdoor air to mix with return air before passing across the
    cooling coil in which case you would only define a single
    VENTILATION type in TRNBuild. When you define the VENTILATION type
    make the air temperature, RH, and flow rate into INPUTS (as opposed
    to scheduled values) and then those inputs will show up in the
    Simulation Studio along with all the other Type56 inputs.<br>
    regards,<br>
     David<br>
     <br>
    <br>
    <div class="moz-cite-prefix">On 5/14/2015 2:57 PM, Anton Åhlund
      wrote:<br>
    </div>
    <blockquote cite="mid:DUB130-W3728C6E57F6FFB4B06050BF0D80@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 12pt;
font-family:Calibri
}
--></style>
      <div dir="ltr">Hi!
        <div><br>
        </div>
        <div>I want to have a scheduled ventilation of a type 56 zone
          with outside air, while at the same time have inputs(Temp,
          Rel.hum. and air flow) for a cooling coil in the same zone.</div>
        <div><br>
          Is this possible? If it is, how can I do it?</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>Best regards,</div>
        <div>Anton Åhlund</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>