[TRNSYS-users] question related to type2
Pascual Ortiz, Carol
carol.pascual at tecnalia.com
Tue Jan 28 01:05:27 PST 2014
Bon dia Angel,
I checked the three points that you mentioned in your previous email and the first option was the one which cause the problem.
I reduced the time step to 30 seconds and the behaviour of the controller improved but as you can imagine the simulations was really slow, so I increased the number of oscillations (controller parameter 1) and now the controller works OK, is it a possibility or I should maintain the number of oscillations in 5?
Thank you very much for your help,
Regards,
Carol
De: Angel Carrera [mailto:angel.carrera at aiguasol.coop]
Enviado el: viernes, 24 de enero de 2014 14:35
Para: TRNSYS users mailing list at the Solar Energy Lab, UW-Madison
Asunto: Re: [TRNSYS-users] question related to type2
Carol,
I forgot one more thing: make sure that the output control function is connected to the same type "input control function", cheers
Angel
2014/1/24 Angel Carrera <angel.carrera at aiguasol.coop<mailto:angel.carrera at aiguasol.coop>>
Egun on Carol,
I think there a two basic reasons for this:
1-The controller gets stuck due to a lack of stability of your model. Parameter 1 sets the number of oscillations that the controller can do in a single time step; if the controller changes of state while trnsys is iterating within a time step, it will never do it (change) more times than the value you have set in parameter 1, so it gets fixed when the number of changes reaches that value. I can't explain it better than it is done in the user help (at least in english), so I recommend you to carefully read the introduction in the controllers section of the mathematical reference on the trnsys help as well as type 2b section. To solve this, usually the best you can do is reduce you time step until you have a coherent behaviour of the controller.
2-The monitoring temperature is governing the controller. If the Input Control Functio (inputs tab of the proforma) exceeds the value of the parameter 2, then the controller output is set to 0.
I imagine that the first possibility is the one explaining that behaviour; reducing the time step is probably a good help for your model, good luck
Angel
2014/1/24 Pascual Ortiz, Carol <carol.pascual at tecnalia.com<mailto:carol.pascual at tecnalia.com>>
Hi TRNSYS user,
In my last simulation I use type 2 on/off differential controllers and I do not know why sometimes it works ok and others doesn´t.
For example Time step temperature control signal
4016,65 25 0
4016,70 25 1
4016,75 25 0
Do you know what I am doing wrong? Does this ever happen to you?
Thank you in advance,
Best regards,
Carol Pascual
Energía Térmica/Thermal Energy
División de Energía y Medio Ambiente/
Energy and Environment Division
TECNALIA
Área Anardi,5
Laida Bidea, Edificio 204
E-20730 Azpeitia - Gipuzkoa (Spain)
T 902 760 000*
M 667119581
T +34 946 430 850<tel:%2B34%20946%20430%20850> (International calls)
carol.pascual at tecnalia.com<mailto:carol.pascual at tecnalia.com>
www.tecnalia.com<http://www.tecnalia.com/>
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
Àngel Carrera
Consultor Senior
Àrea tècnica
[Imagen quitada por el remitente.]
Sistemes Avançats d'Energia Solar Tèrmica SCCL
C/ Roger de Llúria, 29 3r 2a 08009 Barcelona
Mòbil: (+34) 663 27 66 80<tel:%28%2B34%29%20663%2027%2066%2080>
Tel: (+34) 93 342 47 55<tel:%28%2B34%29%2093%20342%2047%2055>
Fax: (+34) 93 342 47 56<tel:%28%2B34%29%2093%20342%2047%2056>
angel.carrera at aiguasol.coop<mailto:angel.carrera at aiguasol.coop>
http://www.aiguasol.coop<http://www.aiguasol.coop/>
--
Àngel Carrera
Consultor Senior
Àrea tècnica
[Imagen quitada por el remitente.]
Sistemes Avançats d'Energia Solar Tèrmica SCCL
C/ Roger de Llúria, 29 3r 2a 08009 Barcelona
Mòbil: (+34) 663 27 66 80
Tel: (+34) 93 342 47 55
Fax: (+34) 93 342 47 56
angel.carrera at aiguasol.coop<mailto:angel.carrera at aiguasol.coop>
http://www.aiguasol.coop<http://www.aiguasol.coop/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140128/df32d213/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ~WRD000.jpg
Type: image/jpeg
Size: 823 bytes
Desc: ~WRD000.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140128/df32d213/attachment-0004.jpg>
More information about the TRNSYS-users
mailing list