Rémi,
a traditional air-to-air heat pump typically has a coefficient of
performance (COP) of about 1.5 to 2 meaning that for every unit of
energy you put into the compressor you deliver about 1.5 to 2 units of
thermal energy to the air stream. So very roughly, your 10kW heat pump
would have a rated heating power between 5 and 7kW. These are very
rough numbers, however and I would highly recommend that you go to the
website of a heat pump manufacturer and find some product literature for
a device with a 10kW heating capacity to see what the heating power
(really the compressor power when in heating mode) is.
Kind regards,
David
On 11/4/2013 03:42, Rémi Marconot wrote:
> Hello Trnsys users,
>
> I would like to simulate an air to air heat pump for a 804m² room by
> using type 954 with the following parameters to have an room
> temperature equal to 20°C
> 10 kW Rated heating capacity
> 5000m³/h Total air flow rate
> No auxilary heating system.
> Outlet air temperature : 37°C
>
> What would be the Rated heating power of such heat pump ?
>
> Thank you for any kind of help in advance.
>
> Rémi
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131104/b3a6bd6c/attachment-0004.htm>
More information about the TRNSYS-users
mailing list