Rémi,<br>
a traditional air-to-air heat pump typically has a coefficient of
performance (COP) of about 1.5 to 2 meaning that for every unit of
energy you put into the compressor you deliver about 1.5 to 2 units
of thermal energy to the air stream. So very roughly, your 10kW heat
pump would have a rated heating power between 5 and 7kW. These are
very rough numbers, however and I would highly recommend that you go
to the website of a heat pump manufacturer and find some product
literature for a device with a 10kW heating capacity to see what the
heating power (really the compressor power when in heating mode) is.<br>
Kind regards,<br>
David<br>
<br>
<br>
<div class="moz-cite-prefix">On 11/4/2013 03:42, Rémi Marconot
wrote:<br>
</div>
<blockquote
cite="mid:18735757.702987.1383558141673.JavaMail.www@wsfrf1224"
type="cite">Hello Trnsys users,<br>
<br>
I would like to simulate an air to air heat pump for a 804m² room
by using type 954 with the following parameters to have an room
temperature equal to 20°C<br>
10 kW Rated heating capacity <br>
5000m³/h Total air flow rate <br>
No auxilary heating system.<br>
Outlet air temperature : 37°C<br>
<br>
What would be the Rated heating power of such heat pump ?<br>
<br>
Thank you for any kind of help in advance.<br>
<br>
Rémi<br>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>