To add to what Jochen wrote, the zones in your Type56 model do not
have to have any direct thermal contact with each other. If you were to
create a zone for the platform, a zone for the concourse and a zone for
the entrance but have no ADJACENT walls in the model then there is no
direct thermal contact between the parts of the building. In order to
simulate the indirect contact (contact through the soil) you need to
implement BOUNDARY walls in each of the three sections of your model
these BOUNDARY walls will be in direct thermal contact with a soil
model. For the soil model I would recommend that you start off simply
assuming that the soil is a known temperature that is not affected by
what happens in the metro. This will get the model running and allow you
to test it. Once you have the building and its thermal zones set up then
you can implement the Type1267 (Tess Ground Coupling -
http://trnsys.com/tess-libraries/individual-components.php) in order to
model the dynamic impact of the soil.
Kind regards,
David
On 11/19/2013 02:57, Cheng Qi wrote:
> Hi,
>
> I have to construct a dynamic building-metro, but only one Type 56 can
> be used in the model. And the metro station has 3 layers (platform,
> concourse, entrance). Given the dynamic soil temperature and tunnel
> temperature, which model is suitable for this situation? Or how can I
> construct this building model?
>
> Regards
> Qi Cheng
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131119/b83958a1/attachment-0001.htm>
More information about the TRNSYS-users
mailing list