<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    Qi,<br>
     To add to what Jochen wrote, the zones in your Type56 model do not
    have to have any direct thermal contact with each other. If you were
    to create a zone for the platform, a zone for the concourse and a
    zone for the entrance but have no ADJACENT walls in the model then
    there is no direct thermal contact between the parts of the
    building. In order to simulate the indirect contact (contact through
    the soil) you need to implement BOUNDARY walls in each of the three
    sections of your model these BOUNDARY walls will be in direct
    thermal contact with a soil model. For the soil model I would
    recommend that you start off simply assuming that the soil is a
    known temperature that is not affected by what happens in the metro.
    This will get the model running and allow you to test it. Once you
    have the building and its thermal zones set up then you can
    implement the Type1267 (Tess Ground Coupling -
    <a class="moz-txt-link-freetext" href="http://trnsys.com/tess-libraries/individual-components.php">http://trnsys.com/tess-libraries/individual-components.php</a>) in order
    to model the dynamic impact of the soil.<br>
    Kind regards,<br>
     David<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 11/19/2013 02:57, Cheng Qi wrote:<br>
    </div>
    <blockquote
cite="mid:CAOdhNBRrv_QKSDaioyzts1WGH5CQa7NKRpPaueujpkjDH-Jqiw@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi,
        <div><br>
        </div>
        <div>I have to construct a dynamic building-metro, but only one
          Type 56 can be used in the model. And the metro station has 3
          layers (platform, concourse, entrance). Given the dynamic soil
          temperature and tunnel temperature, which model is suitable
          for this situation? Or how can I construct this building
          model?</div>
        <div><br>
        </div>
        <div>Regards</div>
        <div>Qi Cheng<br clear="all">
          <div><br>
          </div>
          <br>
          <div>
            <div><br>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>