[TRNSYS-users] Example "SDHW" - how to set max. "temperature to load"?

Michaël Kummert michael.kummert at gmail.com
Thu Feb 14 06:14:36 PST 2013


If you are talking about the standard “SDHW” example, I think Type 11 is in
fact operating correctly, but the plotted TDHW variable is not always
meaningful. Type 11 does not have any thermal mass, so when there is no
flowrate through the tee-piece the outlet temperature is undefined. In that
case Type 11 outputs the temperature at inlet 1 (i.e. the tank temperature,
which is indeed sometimes much higher than 45 °C).

If you add a pipe (or anything with thermal mass) after the tee-piece you
will get a nice constant plot at 45 °C. I am attaching a modified SDHW
example with such an outlet pipe. 

 

Michaël Kummert

Polytechnique Montréal

 

From: trnsys-users-bounces at cae.wisc.edu
[mailto:trnsys-users-bounces at cae.wisc.edu] On Behalf Of Pavel Adam
Sent: Wednesday, February 13, 2013 16:09
To: trnsys-users at cae.wisc.edu
Subject: [TRNSYS-users] Example "SDHW" - how to set max. "temperature to
load"?

 

Hello,

I am trying the example "SDHW" and I do not understand how the divertor
(type 11) works.

I would expect that when the "set point temperature" is set at 45°C, then
the "outlet temperature" from the "tee piece" should be max. 45°C. But it is
not so ... the temperature reaches to the 80 °C.

Can you help me, please? How can I set max. temperature on the outlet from
the "tank" ("temperature to load").

Thank you very much.

Best regards
Pavel Adam
Brno University of Technology

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130214/944f7881/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: SDHW.tpf
Type: application/octet-stream
Size: 266941 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130214/944f7881/attachment-0005.obj>


More information about the TRNSYS-users mailing list