[TRNSYS-users] Error: DataFile for absorption chiller
    Schrade, Johannes 
    Johannes.Schrade at ibp.fraunhofer.de
       
    Mon May 14 08:19:33 PDT 2012
    
    
  
Dear Leon,
first of all you should use decimal points instead of commas within the dat-file.
Then you should check, if you have indicated the right number of independent variables.
In your case, fourth and fifth parameter must be 4, parameter 6 should be 1 and parameter 7 should be 2.
As the minimum number of independent variables per parameter is limited to 2, so that an interpolation can be done, you should include at least a second chilled water set point.
Hope this helps a bit.
Kind regards,
Johannes
Johannes Schrade
Abteilung Wärmetechnik
Fraunhofer-Institut für Bauphysik
Nobelstr. 12
70569 Stuttgart
johannes.schrade at ibp.fraunhofer.de
Telefon 0711 / 970-3416
Telefax 0711 / 970-3399
www.ibp.fraunhofer.de/wt/
Johannes Schrade
Department Heat Technology 
Fraunhofer Institute for Building Physics
Nobelstr. 12
70569 Stuttgart, Germany
johannes.schrade at ibp.fraunhofer.de
Phone +49 711 / 970-3416
Fax +49 711 / 970-3399
www.ibp.fraunhofer.de/wt/
-----Ursprüngliche Nachricht-----
Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von Leon Becker
Gesendet: Montag, 14. Mai 2012 11:30
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Error: DataFile for absorption chiller
Hey everybody,
I have written a dat. file for a type 107 absorption chiller. But when I start the simulation it can't read my file.
TRNSYS Message    109 : Error reading data stored in logical unit. NOTE: the reported logical unit number may be automatically or internally ASSIGNed, or you may have specified the incorrect number of independent variables.  Information supplémentaire : Numéro de fichier (UNIT) 35
I've attached the file. Does anyone have an idea why it doesn't work?
Thanks. You all have a great day.
Leon
    
    
More information about the TRNSYS-users
mailing list