[TRNSYS-users] Problem with Type 11
David BRADLEY
d.bradley at tess-inc.com
Fri Jul 13 13:55:50 PDT 2012
Michela,
The error is coming from Type56. When you define an active layer in
Type56, the specific flow rate in that layer (kg/h.m2) must be above a
certain minimum in order for the energy transfer algorithms to be valid.
The error states that the flow rate in the active layer of surface 44 in
your building is too low. Look carefully at the way you are setting the
flow rate that comes through your network of Type11s and makes sure that
each branch that feeds an active layer always has sufficient flow in it.
Regards,
David
On 7/10/2012 10:19, michela canneori wrote:
> Dear all,
> I have a problem with Type 11.
> My problem is the follow:
> in the listing file I read a fatal error in the unit 28, but I haven't
> any indications for this.
> I attach the listing file and the messages that I read because I hope
> that someone can help me.
> Thanks.
> Regards
> Michela.
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120713/879bc810/attachment-0005.htm>
More information about the TRNSYS-users
mailing list