    Michela,<br>
      The error is coming from Type56. When you define an active layer
    in Type56, the specific flow rate in that layer (kg/h.m2) must be
    above a certain minimum in order for the energy transfer algorithms
    to be valid. The error states that the flow rate in the active layer
    of surface 44 in your building is too low. Look carefully at the way
    you are setting the flow rate that comes through your network of
    Type11s and makes sure that each branch that feeds an active layer
    always has sufficient flow in it.<br>
    Regards,<br>
     David<br>
    <br>
    <div class="moz-cite-prefix"><br>
      On 7/10/2012 10:19, michela canneori wrote:<br>
    </div>
    <blockquote
cite="mid:CAH=8v9MvyC8Y0E+ft3O_qf-u8qWNieqh7dP7tFeC=em8uetWFQ@mail.gmail.com"
      type="cite">
      <div>Dear all,</div>
      <div>I have a problem with Type 11.</div>
      <div>My problem is the follow:</div>
      <div>in the listing file I read a fatal error in the unit 28, but
        I haven't any indications for this.</div>
      <div>I attach the listing file and the messages that I read
        because I hope that someone can help me.</div>
      <div>Thanks.</div>
      <div>Regards</div>
      <div>Michela.</div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@cae.wisc.edu">TRNSYS-users@cae.wisc.edu</a>
<a class="moz-txt-link-freetext" href="https://mailman.cae.wisc.edu/listinfo/trnsys-users">https://mailman.cae.wisc.edu/listinfo/trnsys-users</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
    <br>
    <br>
  </body>
</html>