Stefano,
>
> Why is not the button "Divide surface" always present?
>
> I am simulating a radiant wall with "standard" features (pipe spacing
> 15 cm, pipe ext diameter 2 cm, pipe thickness 2 mm).
>
the "divide surface" button is only needed if TRNBuild calculates that
the specific mass flow rate (kg/h.m2) of the floor you are proposing is
below the allowable limit. If the specific flow rate is below 13 kg/h/m2
then you have to segment the floor into multiple floors in series (and
the "divide surface" button will become active.
>
> Furthermore, I have found no information about how the parameter
> "number of fluid loops" is taken into account in the mathematical
> model. Do you have any idea?
>
> Last question: how does TRNSYS calculate the minimum allowed inlet
> mass flowrate in case of a "number of fluid loops" greater than 1?
>
I am not sure about these but have forwarded the question on to our
Transsolar colleagues. I will let you know as soon as I hear back from them.
Best,
David
--
***************************