    Stefano,<br>
    <span style="font-family:"Trebuchet
      MS","sans-serif""><o:p></o:p></span>
    <blockquote
      cite="mid:EF650F471C832344BEBD07E6C0E0DB3F178241E0@abz02be.eurac.edu"
      type="cite">
      <div class="WordSection1">
        <p class="MsoNormal"><span style="font-family:"Trebuchet
            MS","sans-serif"">Why is not the button
            “Divide surface” always present?<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-family: "Trebuchet
            MS","sans-serif";">I am simulating a radiant
            wall with “standard” features (pipe spacing 15 cm, pipe ext
            diameter 2 cm, pipe thickness 2 mm).</span></p>
      </div>
    </blockquote>
    the "divide surface" button is only needed if TRNBuild calculates
    that the specific mass flow rate (kg/h.m2) of the floor you are
    proposing is below the allowable limit. If the specific flow rate is
    below 13 kg/h/m2 then you have to segment the floor into multiple
    floors in series (and the "divide surface" button will become
    active.<br>
    <blockquote
      cite="mid:EF650F471C832344BEBD07E6C0E0DB3F178241E0@abz02be.eurac.edu"
      type="cite">
      <div class="WordSection1">
        <p class="MsoNormal"><span style="font-family:"Trebuchet
            MS","sans-serif""><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-family:"Trebuchet
            MS","sans-serif""><o:p> </o:p>Furthermore, I
            have found no information about how the parameter “number of
            fluid loops” is taken into account in the mathematical
            model. Do you have any idea? <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="font-family: "Trebuchet
            MS","sans-serif";">Last question: how does
            TRNSYS calculate the minimum allowed inlet mass flowrate in
            case of a “number of fluid loops” greater than 1?</span></p>
      </div>
    </blockquote>
    I am not sure about these but have forwarded the question on to our
    Transsolar colleagues. I will let you know as soon as I hear back
    from them.<br>
    Best,<br>
     David<br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>