[TRNSYS-users] Adding door TRNSYS 3d
    David BRADLEY 
    d.bradley at tess-inc.com
       
    Tue Oct 18 07:49:47 PDT 2011
    
    
  
Karol,
  I typically ignore the doors in residential modeling.
  The problem with defining a door as a window is that since it is a 
window, it will allow solar radiation to transmit into the residence. Of 
course if you have a glass door on the house, that is entirely 
appropriate. However, if you have an opaque door, it is better to define 
the door as a different wall section.
The following steps usually work for me in Trnsys3D, :
1. create the zone that contains the exterior door and make sure that 
the zone is active.
2. draw the door, starting from the bottom edge of the zone. Once you 
complete the door, Trnsys3d will "recognize" it as a window.
3. with the zone still active, select the window surface (just the 
bluish part, not the lines that define the size of the window).
4. delete the surface - you should now have a wall with a big hole in it.
5. retrace the line that defines the top of the door - Trnsys3D usually 
now "regnognizes" this as a door.
Once you import the *.idf into TRNBuild, you're going to have to be 
careful because both the "door" and the wall surrounding it will get set 
as walltype EXT_WALL. You will need to define a wall construction in 
TRNBuild for your door (probably using a single "massless" layer) and 
then you will need to change the door surface from walltype EXT_WALL to 
your newly created walltype "DOOR"
Kind regards,
  David
On 10/18/2011 03:17, Karol Bandurski wrote:
>
> Nidal and David,
>
> I'm not sure if I understand problem, but I have just create 
> single-family house and I modeled only exterior door.
>
> I defined this door as window and create this door using WINDOW 6 
> (software of Lawrence Berkeley National Laboratory -- free download): 
> u-value=2.6 W/m^2K and g-value=0.144
>
> It seems to me that interior door are also possible to define this way.
>
> It seems to me that in Google SketchUp edge of window/door can't 
> overlap with edge of wall. To respect this you can make door which 
> begin a few centimeters above lower edge of wall
>
> I'm beginner in TRNSYS, so I'm not sure if my ideas are well!!!
>
> I enclose pdf  with instruction how to create window in WINDOW and 
> introduce it to TRNBuild library.
>
> Good luck
>
> ------------------------------------------------
>
> Karol Bandurski MSc.
>
> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>
>
> Poznan University of Technology
>
> www.ee.put.poznan.pl <http://www.ee.put.poznan.pl/>
>
> www.put.poznan.pl <http://www.put.poznan.pl/>
>
> *From:*David BRADLEY [mailto:d.bradley at tess-inc.com]
> *Sent:* Monday, October 17, 2011 6:34 PM
> *To:* Nidal Abdalla
> *Cc:* TRNSYS-users
> *Subject:* Re: [TRNSYS-users] Adding door TRNSYS 3d
>
> Nidal,
>   This is a bit of a problem in the Trnsys3D plugin; the developers 
> are working on a solution. I have had some success in breaking my wall 
> up into a "wall" part and a "door" part but this can be tricky because 
> you don't want the door to get recognized as a window. I then set the 
> two parts as different wall types and take care of correcting the 
> construction in TRNBuild.
>   If there are not very many doors in your zone, I would recommend 
> that you just ignore them. I only took them into account because I was 
> simulating a garage that had well insulated wall and completely 
> uninsulated (very large) garage doors.
> Best,
>  David
>
>
> On 10/17/2011 05:55, Nidal Abdalla wrote:
>
> Dear All
>
> I am working with multi-zone building using TRNbuild, and I wonder if 
> you can help me how I can add or identify a DOOR to the one zone building.
>
> Also I could'nt add or identify a door by using Trnsys3D.
>
> Best Regards
>
> Nidal Abdalla
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu  <mailto:TRNSYS-users at cae.wisc.edu>
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
> -- 
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI  53703 USA
>   
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com  <mailto:d.bradley at tess-inc.com>
>   
> http://www.tess-inc.com
> http://www.trnsys.com
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com