[TRNSYS-users] PID controller in TRNSYS developer
marcello.caciolo at aximaseitha-gdfsuez.com
marcello.caciolo at aximaseitha-gdfsuez.com
Wed Nov 16 07:14:03 PST 2011
Dear Wang,
As I used the PID control many times, I am sure that there is no problem with the code…I suggest you to check the following two points:
1) Concentration unit: it happened to me to make trivial errors because of the expression of concentration: check if the output of your model is not expressed in percent or per mille instead of ppm;
2) Input 11 (Fraction of ySet for proportional effect) should be set to zero and parameter 1 (mode) to zero.
In addition, you should plot the output 2 and 4 in order to understand where the problem is. Output 2 should be equal to set-point concentration minus actual concentration, output 4 to output 2 multiplied by kp.
Good luck!
Best regards,
Marcello
De : wanghongyang1767 at gmail.com [mailto:wanghongyang1767 at gmail.com] De la part de wangyang
Envoyé : mercredi 16 novembre 2011 13:00
À : Caciolo Marcello (Axima Seitha);; hotline at transsolar.com
Objet : Re: [TRNSYS-users] PID controller in TRNSYS developer
Dear marcello.caciolo,
Many thanks for your quick reply!
I know and understand all what you explained. Since my profession for Bachelor and Master is Automation control. That is also the reason why I suspect the function of PID controller in TRNSYS. As you said, I tried many time the gain Kp and integral time Ki and small time step 1 min or smaller in order to avoid oscillations, a large difference between the set point 1000 ppm and actual CO2 concentration etc.
I mentioned already as my first email about PID controller: I set the set point CO2 concentration 1000 ppm as PID controller's set point; its control signal links to Opening Factor (OF) of windows; indoor CO2 concentration links to PID's controlled variable. However, when indoor CO2 concentration is less than set point 1000 ppm, PID begins to activate OF i.e. windows are open. Based on PID principle, control signal should be set to zero. BUT it is not like this. As we know, if CO2 concentration is not getting to set point 1000 ppm, at this time windows are open will result in the ERROR (between the set point and actual indoor CO2 concentration) increasing. So I'm puzzled! So I suspect the function of PID controller in TRNSYS.
Now, I only would like a solution for this problem as I said in recent emails and the adequate explanations for this OF_CO2 concentration_PID control issue in TRNSYS .
Many thanks in advance!
br
wang
2011/11/16 <marcello.caciolo at aximaseitha-gdfsuez.com<mailto:marcello.caciolo at aximaseitha-gdfsuez.com>>
Dear Wang,
I find that your problem description is not very clear, but I try anyway to guess what you want to do.
In my understanding, if you want CO2 concentration to be less than 1000 ppm, you should use a PID control with a positive gain and an output signal between 0 and 1, directly connected to the OF. In this way, if the CO2 concentration is less than 1000 ppm, the error (and integral and derivative part of the signal, if present) of the PID control will be negative, so that control signal is set to zero. On the other hand, when CO2 concentration is above 1000 ppm, the error is positive and the output signal will be more than 0, so opening the window.
Take care to the choice of the gain of the PID: a too high value could generate oscillations, while a value too low will lead to a large difference between actual and setpoint CO2 concentration. Also note that, without an integral part, the PID control is purely proportional and will always lead to a CO2 concentration higher than 1000 ppm. However, the integral time should be high enough to prevent oscillations. The time period should be also short enough in order to avoid instabilities in control.
Guessing a good value of the gain and the integral time of a PID needs to wall understand the main principles of a proportional and integral controller. I suggest you to have a look to some textbooks about HVAC control in order to understand these principles.
I hope that these explanation will help you.
Best regards,
Marcello CACIOLO
Responsable Outils et Méthodes d'Analyse Energétique
___________________________________________________
Erreur ! Nom du fichier non spécifié.
Cellule Efficacité Energétique
Direction Commerciale
46 Boulevard de la Prairie au Duc BP 40119
44000 Nantes Cédex 2
Tel. 02 40 41 06 57
mail: marcello.caciolo at aximaseitha-gdfsuez.com<http://marcello.caciolo@aximaseitha-gdfsuez.com>
www.aximaseitha-gdfsuez.com<http://www.aximaseitha-gdfsuez.com/>
P Pensez à l'environnement avant d'imprimer ce message
De : trnsys-users-bounces at cae.wisc.edu<mailto:trnsys-users-bounces at cae.wisc.edu> [mailto:trnsys-users-bounces at cae.wisc.edu<mailto:trnsys-users-bounces at cae.wisc.edu>] De la part de wangyang
Envoyé : mercredi 16 novembre 2011 10:53
À : David BRADLEY; trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>; hotline at transsolar.com<mailto:hotline at transsolar.com>
Objet : Re: [TRNSYS-users] PID controller in TRNSYS developer
Dear David,
As I said yesterday, I linked PID's output Control Signal to a minus 1 then to OF. The results are still very WEIRD. OF becomes minus value which is not reasonable very much i.e. the window is open towards abnormal direction; CO2 concentration is not decreasing as we hoped, however, it is becoming much more bigger e.g. 4000 ppm.
Now, I only would like a solution for this problem as I said in last email and the adequate explanations for this OF_CO2 concentration_PID control issue.
Many thanks in advance!
br
wang
2011/11/15 王洋 <wanghongyang1767 at gmail.com<mailto:wanghongyang1767 at gmail.com>>
Dear David,
Many thanks for your reply!
I already saw both of them as you mentioned, however, they are not helpful for my simulation results i.e. they don't explain the things I wanted.
Your heating/cooling example is very vivid. Do you mean I need add an equation after the PID i.e. link PID's output Control Signal to a minus 1 then to OF?
Now, I only would like a solution for this problem as I said in last email and the adequate explanations for this OF_CO2 concentration_PID control issue.
Many thanks in advance!
br
wang
2011/11/14 David BRADLEY <d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>>
Wang,
You should already have the source code for the PID controller in ..\TrnsysXX\SourceCode\Types\. I would also recommend reading the Type23 section of the 04-MathematicalDescription manual.
PID controllers can operate in one of two ways: they can generate a greater signal value if the sampled input value is below the set point or they can generate a greater signal value if the sampled input is above the current set point. Imagine a heating application with a PID controller. As the zone temperature falls, you want the PID to give you a bigger and bigger signal. Now imagine a cooling application. As the zone temperature rises, you want the PID to give you a bigger and bigger signal. You may have to add an equation after the PID to invert its control signal if it is acting the opposite of the way that you want.
David
On 11/14/2011 04:28, wangyang wrote:
Dear all,
I have a question about PID controller in TRNSYS for its developer.
Which expert knows PID controller in TRNSYS developer? Or Which expert could pass me the source code of PID controller or its internal algorithm etc.? I guess PID controller in TRNSYS is based on empirical equation or iterative algorithm. Since there is very weird simulation results i.e. I set the set point CO2 concentration 1000 ppm as PID controller's set point; its control signal links to Opening Factor (OF) of windows; indoor CO2 concentration links to PID's controlled variable. However, when indoor CO2 concentration is less than set point 1000 ppm, PID begins to activate OF i.e. windows are open. But based on PID principle, as we know, if CO2 concentration is not getting to set point 1000 ppm, at this time windows are open will result in the ERROR (between the set point and actual indoor CO2 concentration) increasing. So I'm puzzled! Please PID controller in TRNSYS developer or other experts explain this weird phenomenon!
Many thanks in advance!
br
wang
2011/11/12 <trnsys-users-request at cae.wisc.edu<mailto:trnsys-users-request at cae.wisc.edu>>
Send TRNSYS-users mailing list submissions to
trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>
To subscribe or unsubscribe via the World Wide Web, visit
https://mailman.cae.wisc.edu/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
trnsys-users-request at cae.wisc.edu<mailto:trnsys-users-request at cae.wisc.edu>
You can reach the person managing the list at
trnsys-users-owner at cae.wisc.edu<mailto:trnsys-users-owner at cae.wisc.edu>
When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Today's Topics:
1. Re: (no subject) (David BRADLEY)
2. Re: TRNSYS3D Shading on Walls? (David BRADLEY)
3. Re: how to identify a wall that is adjacent two walls
(David BRADLEY)
4. Error in reading type 51 external performance File
(Walif M'kacher)
---------- 已转发邮件 ----------
From: David BRADLEY <d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>>
To: Erik Boschek <erikboschek at yahoo.com<mailto:erikboschek at yahoo.com>>
Date: Fri, 11 Nov 2011 12:01:47 -0600
Subject: Re: [TRNSYS-users] (no subject)
Erik,
You are right on with all three of your points. For reference, we discontinued use of Type109 in Trnsys17 in favor of option 2 (Type15), which is correct from an energy perspective even though it isn't a smooth curve. In gernal think that a control strategy that relies only on the instantaneous DNI as its input might run into trouble not only in simulation but also in the real world; clouds pass in front of the sun rapidly sometimes. While I won't pretend that the "spiky" profile that Type15 generates is totally realistic, I think it is a fairly accurate representation of DNI. Bear in mind that Type15 is trying to reconstruct a minute by minute radiation profile based only on 1 number and to do so correctly for all possible climate types. You might consider a control strategy that uses the output of Type15 but put through a running-average component so that your control decisions are based on a somewhat more stable (smoother) profile.
Best,
David
On 11/11/2011 00:32, Erik Boschek wrote:
Dear TRNSYS users,
I have a simple question regarding weather reading and interpolating direct normal radiation (DNI) values for time steps less than an hour.
As long as I have been using TRNSYS (using TRNSYS 16.1) I have understood this can be done in a few ways as follows, including the consequence for an example TM2 file (see attached screen shot for clarification):
1.) Do not interpolate, using Type 15 with output DNR (not interpolated): you end up with a "steppy" profile
2.) Using Type 15, but with 2-axis tracking and the output "Beam radiation for surface": you get a discontinuous "spikey" profile, but the integration of energy across the hour is respected
3.) Same as 2, but using Type109-TMY2: You get a smooth profile, but often there appear inexplicable spikes at the beginning or end of the day. The one in the plot obviously is an extreme case.
For reference: I just used the Daggett profile "US-CA-Daggett-23161.tm2" which came with TRNSYS, but the behavior is not specific to this file.
Generally, I have been using 2, but it can cause problems if there is, for example, some triggering function based on DNI and the DNI hovers around the threshold. Is there another option for getting a smoother profile or is it best just to not interpolate? Any opinions? Feel free to point me to an earlier post on this topic in case I missed it.
Thanks,
Erik Boschek
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577<tel:%2B1.608.274.2577>
F:+1.608.278.1475<tel:%2B1.608.278.1475>
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com<http://www.tess-inc.com/>
http://www.trnsys.com<http://www.trnsys.com/>
---------- 已转发邮件 ----------
From: David BRADLEY <d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>>
To: Marion Hiller <hiller at transsolar.com<mailto:hiller at transsolar.com>>
Date: Fri, 11 Nov 2011 12:03:16 -0600
Subject: Re: [TRNSYS-users] TRNSYS3D Shading on Walls?
TRNSYS-users,
My apologies; my reply to Graham was incorrect; as Marion says, only the windows are affected.
Kind regards,
David
On 11/11/2011 01:33, Marion Hiller wrote:
Graham,
the shading defined in Trnsys3D effects only windows.
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0<tel:%2B%2049.711.67976.0>
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
-----Ursprüngliche Nachricht-----
Von: Graham Linn [mailto:grahamjlinn at gmail.com<mailto:grahamjlinn at gmail.com>]
Gesendet: Donnerstag, 10. November 2011 21:49
An: trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>
Betreff: [TRNSYS-users] TRNSYS3D Shading on Walls?
Hello TRNSYS users,
I have a question about shading in TRNSYS3D. Does a shading object
affect how much insolation hits the entire building or just the
windows on the building?
Thank you!
Graham
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577<tel:%2B1.608.274.2577>
F:+1.608.278.1475<tel:%2B1.608.278.1475>
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com<http://www.tess-inc.com/>
http://www.trnsys.com<http://www.trnsys.com/>
---------- 已转发邮件 ----------
From: David BRADLEY <d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>>
To: Nidal Abdalla <nidalabdalla at yahoo.com<mailto:nidalabdalla at yahoo.com>>
Date: Fri, 11 Nov 2011 12:29:48 -0600
Subject: Re: [TRNSYS-users] how to identify a wall that is adjacent two walls
Nidal,
You have to be a little careful here. If you have a wall in zone 1, half of which is adjacent to zone 2 and half of which is adjacent to zone 3, you actually need to draw the wall as two walls in zone 1. Trnsys3D requires the user to be quite vigilant about manually setting adjacencies. You need to draw the ADJACENT wall in both zones and you need to open the object window for each of them, set the construction to ADJ_WALL, set the "outside boundary condition" to "Zone" and then manually select the zone to which it is adjacent in the "outside boundary object" field.
If you have been very careful about drawing your ADJACENT walls so that they have exactly the same verticies in both zones to which they belong, you can then select the menu item: Plugins: Trnsys3d: Surface Matching and click the "match in entire model" button.
Kind regards,
David
On 11/11/2011 08:32, Nidal Abdalla wrote:
I drew a house using Trnsys3d that consists of: 3 bed rooms, living room, guest room and bath . The house was divided into 6 zones. Wall_zone5, for example, is adjacent two walls for two different zones. I am wondering how to identify a wall (using Object Info) that is adjacent two or more walls of diff. zones.
Best Regards
Nidal Abdalla
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577<tel:%2B1.608.274.2577>
F:+1.608.278.1475<tel:%2B1.608.278.1475>
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com<http://www.tess-inc.com/>
http://www.trnsys.com<http://www.trnsys.com/>
---------- 已转发邮件 ----------
From: "Walif M'kacher" <walif.mkacher at gmail.com<mailto:walif.mkacher at gmail.com>>
To: trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>
Date: Sat, 12 Nov 2011 15:13:05 +0100
Subject: [TRNSYS-users] Error in reading type 51 external performance File
Dear TRNSys Users,
I have a problem with external file of type 51a (cooling tower with an external performance File):
That the simulation with this type causes error and this can't read this external file (.txt)
Would you please help me how to correct the file joined or send me a truth format of this .txt file
Many thanks in advance
Mkacher Walif
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577<tel:%2B1.608.274.2577>
F:+1.608.278.1475<tel:%2B1.608.278.1475>
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com<http://www.tess-inc.com/>
http://www.trnsys.com<http://www.trnsys.com/>
GDF SUEZ Mail Disclaimer: http://www.gdfsuez.com/disclaimer/disclaimer-fr.html
GDF SUEZ Mail Disclaimer: http://www.gdfsuez.com/disclaimer/disclaimer-fr.html
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20111116/e75692a6/attachment-0001.htm>
More information about the TRNSYS-users
mailing list