[TRNSYS-users] window pane temperature diverging
David BRADLEY
d.bradley at tess-inc.com
Wed Jan 19 07:40:22 PST 2011
Thomas,
I've run into this problem a few times; it essentially means that the
calculations going on inside Type56 to resolve all the gas and pane
temperatures in your window are not converging. I have often had success
by changing the inside surface convection coefficient calculation from
"automatic" to "constant" in the window type manager for whichever
window is giving problems. A typical value for the a constant inside
convection coefficient is 11 kJ/h.m2. This is not an ideal solution
because of course the convection coefficient changes as the window pane
and room temperature change but it does stabilize the calculations some.
Also make sure that you do not accidentally have something strange
going on in the zone (huge gains, moisture loads, infiltration, or
ventilation) and that your zone capacitance is set to about
ZoneVolume*1.2*1.007*5.
Kind regards,
David
On 1/19/2011 08:15, Thomas Bockelandt wrote:
>
> Dear all,
>
> I am currently simulating an office building in trnsys but i keep
> getting the following error:
>
> *** Warning at time : 56.000000
>
> Generated by Unit : 88
>
> Generated by Type : 56
>
> Message : Zone 6 surface 141 pane temperature
> calculation is diverging at time 56.00000TDIF:
> 3.55469 ITPANE: 31 ITCALC: 1
>
> And this for all windows in my b17-file,giving me a fatal error.
>
> I checked the links with my weather data reader (meteonorm) multiple
> times and have even changed the type of data reader entirely but the
> warnings/error remains, always after 56 hours.
>
> I never had this error before, while I used the data reader-type 56
> configuration numerous times before.
>
> Does anyone know where this error might come from?
>
> Best regards,
>
> *Thomas Bockelandt*
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110119/40822bea/attachment-0001.htm>
More information about the TRNSYS-users
mailing list