[TRNSYS-users] Type 56 help
Adrien JEZEQUEL - ITF
a.jezequel at itf.biz
Mon Apr 4 01:50:21 PDT 2011
Dear Devin,
Your active layer have to be placed between two layers. As written in
the manual, "the thickness of both layers adjacent to active layer must
be >= 0.3 * pipe spacing".
Regarding the convective coefficient, you will have to select "internal
calculation" in "Convective Heat Transfer coefficient of wall" in
Type56 wall type manager. This option is available for all type of wall,
except from back side of external walls.
You may also have a look to the manual for more informations : "TRNSYS
16 Multizone Building Modelling with Type 56 and TRNBUILD" p 6-44.
Best regards
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz ou aj at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
Le 03/04/2011 18:06, Devin Rohan a écrit :
> I'm using TRNSYS version 16 to model a radiant floor heating system
> for a single office zone/room. I have 2 questions.
>
> 1) When I try and create a new active layer in Type 56 (multi-zone
> building), I get the following warning/error message...
>
> *"active layer could not place on first position."* What does this
> mean and how can it be fixed?
>
> 2) Is there a better way to model a single zone than Type 56's GUI. I
> also want to have the convective heat transfer coefficients calculated
> internally for every time step (since they depend on the varying
> surface temperatures), but Type 56 only allows this if the wall is
> classified as "Internal" and not "External". How can I account for
> the varying convective heat transfer coefficients?
>
> Thank you
>
> --
> Devin M. Rohan, LEED Green Associate
> Purdue University
> Civil/Architectural Engineering
> drohan at purdue.edu <mailto:drohan at purdue.edu>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110404/9af89422/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_2010.jpg
Type: image/jpeg
Size: 17526 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20110404/9af89422/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list