[TRNSYS-users] Overall heat transfer values of walls

Mariëlle Nuchelmans M.Nuchelmans at chri.nl
Tue Sep 28 23:10:21 PDT 2010


The reference U-value is calculated with standard convective heat transfer coefficient. So it you change this coefficient, the U-value changes while calculating, but the indicated value stays the same (but it doesn't calculates with this value) 

The standard values are: inside: 7,7 outside: 25 (radiation coefficient included)

Kind regards,

Mariëlle 

Van: a8304506 at graduate.hku.hk [mailto:a8304506 at graduate.hku.hk] 
Verzonden: woensdag 29 september 2010 2:26
Aan: Trnsys discussion group
Onderwerp: [TRNSYS-users] Overall heat transfer values of walls

Hello, everyone.

When I edit a wall type in Type56, there is a u-value indicated with the remark
"for reference only".  What is the meaning for this u-value?  It seems that
this figure does not change even if I use different values for the convective
heat transfer coefficient for the wall.  If I want to know the actual overall
heat transfer of the wall, how can I find it?  Please advise.  Thank you!

Best Regards
LEE, Chun Kwong
Division of Building Scienece and Technology
City University of Hong Kong









More information about the TRNSYS-users mailing list