[TRNSYS-users] Re : Problem with windows lib
Marion Hiller
hiller at transsolar.com
Thu Jul 22 02:00:31 PDT 2010
Damien,
Window 4002, 4102, 4202 and 4302 differ only in size.
The window data was created without spectral data. TRNSYS 16 uses a 2
band model (visual and nonvisual) and windows created
without spectral data may cause this problem. Windows with an ID lower
than 9999 are included in the library for backwards compatibility
reasons.
For solving the problem, you may modify properties of the window data in
your BUI by an editor.
I suggest NOT to edit the BASIC library itself. This may leed to
confusion.
For solving the error message TRNSYS calculated a one band model (solar)
only by setting
values for Tvis = Tsol, Rfvis = Rfsol and Rbis = Rbsol of the window
data in the BUI file.
Tsol 0.268 0.270 0.263 0.253 0.243 0.223 0.183 0.116 0.042 0.000 0.207
Abs1 0.327 0.330 0.339 0.345 0.347 0.351 0.367 0.380 0.313 0.001 0.347
Abs2 0.066 0.066 0.067 0.068 0.070 0.071 0.070 0.064 0.051 0.000 0.067
Abs3 0.108 0.110 0.112 0.113 0.110 0.107 0.101 0.082 0.041 0.000 0.100
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.231 0.223 0.220 0.221 0.230 0.247 0.279 0.357 0.554 0.999 0.269
Rbsol 0.231 0.223 0.220 0.221 0.230 0.247 0.279 0.357 0.554 0.999 0.269
Tvis 0.625 0.632 0.615 0.595 0.570 0.523 0.425 0.265 0.097 0.000 0.484
Rfvis 0.137 0.125 0.121 0.125 0.142 0.172 0.226 0.336 0.554 0.999 0.199
Rbvis 0.137 0.125 0.121 0.125 0.142 0.172 0.226 0.336 0.554 0.999 0.199
However, what you want to simulate is window with a very low
conductivity.
You may modify the conductivity of the glas panes "Cond(W/m2-C ) "
for reducing the total u value in the BUI file.
Layer ID# 9061 9052 9062 0 0 0
Tir 0.000 0.000 0.000 0 0 0
Emis F 0.840 0.840 0.070 0 0 0
Emis B 0.070 0.840 0.840 0 0 0
Thickness(mm) 4.0 4.0 4.0 0 0 0
Cond(W/m2-C )225.0 225.0 225.0 0 0 0
Spectral File None None None None None None
Best,
Marion
_____
Von: Damien Palacios [mailto:pseudomino at rocketmail.com]
Gesendet: Mittwoch, 21. Juli 2010 17:58
An: David Bradley
Cc: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Re : Problem with windows lib
Yes,
my TRNSYS version is 16.
As for the windows ID, all those with an u-value of 0.4 are causing the
same error, in my model : 4002, 4102, 4202, 4302.
I join the files needed in a .rar.
Thanks
_____
De : David Bradley <bradley at tess-inc.com>
À : Damien Palacios <pseudomino at rocketmail.com>
Cc : trnsys-users at cae.wisc.edu
Envoyé le : Mer 21 juillet 2010, 16h 37min 37s
Objet : Re: [TRNSYS-users] Problem with windows lib
Damien,
Could you please specify which version of TRNSYS you are using and
which window ID you chose (there are a number of different windows in
the win4lib.dat file). Please also send your *.tpf, *.bui (or *.b17),
and *.lst files as well as any others that would be needed in order to
run the project.
Best,
David
On 7/21/2010 05:36, Damien Palacios wrote:
Hello,
TRNSYS returns be plenty of these errors in listing result file :
winlib reader: incorrect selectivity of visual+solar transmission
caused a negative value for nonvisual Transmission Tra_ang_nonvis =
-0.045 for Window-ID 4202 at an angle of 30 ° Tra_ang_nonvis
is set to 0 for this angle
I use the library
C:\Program Files\Trnsys16\Building\Lib\Basic\W4-lib.dat
Actually, I would need a window with a u-value of 0.1 kJ/h/m²/K , and
because there are not such window, I use the smallest value : 0.4.
But for each of the windows with this value, I have the same error.
Can you help me? At least to know why does this message appears?
Note: the issue is the same if I try in American\W4-lib.dat,
German\W4-lib.dat...
Have a nice day!
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100722/98f4f579/attachment-0001.htm>
More information about the TRNSYS-users
mailing list