Hello,

You are absolutely right about this. There is a mismatch between 
documentation and example datafile on one side and source code on the 
other. The first column in the datafile should consist of COP ratios, 
while the second column should consist of capacity ratios. There have been 
some postings about this on the list in the past.

Best regards,
Knut Erik Enerstvedt

 

>Hello, all.

>I previously developed a parametric model for a water-cooled chiller.  I 
used it
>to compare the results with those based on Type666.  I then found that
>calculated COP seemed to increase only mildly during the low-load period 
when
>using Type666.  I went through the source code and the related data 
files.  I
>found that the following statements appeared to be wrong:

>COP_RATIO=Y(1)
>CAP_RATIO=Y(2)

>According to the data file, the first output should be the capacity ratio 
while
>the second output is the COP ratio.  The same case happened for Type655. 
Am I
>wrong?

>Best Regards
>LEE, Chun Kwong
>Division of Building Science and Technology
>City University of Hong Kong
------------------------------------------------------------------------------------------------------------