[TRNSYS-users] Internal and external shading factors in Type 56
    Kersken, Matthias 
    Matthias.Kersken at ibp.fraunhofer.de
       
    Thu Nov 12 02:02:53 PST 2009
    
    
  
Dear Knut!
 
When modelling a internal shading together with a large glazing in a
TRNSYS-versions below 17 You have to consider the following!
 
Once the solar radiation as crossed one of Your two zones and (a part of it)
has enters the second zone all the radiation will be threaded as diffuse
radiation.
If You don't use geosurf-factors all the beam-radiation entering entering
the second zone directly will also be handled as diffuse (so set a geosurf
at least in the lower zone !)
and at least You also have the diffuse radiation entering the second zone
directly.
This means in a two-zone-green-house-model You have a very high amount of
diffuse radiation in the zones (of course this effect exists in both
directions between the two zones).
 
Now the (high) diffuse radiation in the zone is distributed equal to every
m² of zone-wall and windows, this means much more radiation is distributed
back to the glazing (where it came from) as it would be in reality and so
more energy leafs through the glazing as it would in reality.
If the internal shading is active it keeps this high amount of radiation
inside the room and so You may have effects like the room temperature as a
light drop for a moment, when You deactivate Your int. shading.
This may explain Your steep temperature changes (?).
A solution for this problem I don not have at hand (except TRNSYS 17) but
You my try using a low inside reflection of Your shading, this might reduce
this effect.
 
I think Your assumption concerning the heat transmission in the night being
influenced by the thermal resistance of the shading is correct.
This effect is' expectable and in already worked with it in TRNSYS (16).
 
With kind regards,
    Matthias Kersken
---
 
Dipl.-Ing. Matthias Kersken
Wissenschaftlicher Mitarbeiter / Abteilung Energiesysteme
Fraunhofer-Institut für Bauphysik 
Institutsteil Holzkirchen
Fraunhoferstraße 10
83626 Valley
eMail: Matthias.Kersken at ibp.fraunhofer.de
Telefon 08024 / 643-204
Telefax 08024 / 643-366
www.ibp.fraunhofer.de <http://www.ibp.fraunhofer.de/> 
Dipl.-Ing. Matthias Kersken
Research Associate / Department Energy Systems 
Fraunhofer Institute for Building Physics 
Branch Holzkirchen
Fraunhoferstraße 10
D-83626 Valley
eMail:  <mailto:Matthias.Kersken at ibp.fraunhofer.de>
Matthias.Kersken at ibp.fraunhofer.de
Phone +49 8024 / 643-204
Fax +49 8024 / 643-366
 <http://www.ibp.fraunhofer.de/> www.ibp.fraunhofer.de
 
 
 
 
 
 
 
 
 
 
 
 
 
---
 
  _____  
Von: knut.erik.enerstvedt at niva.no [mailto:knut.erik.enerstvedt at niva.no] 
Gesendet: Dienstag, 10. November 2009 10:11
An: trnsys-users at engr.wisc.edu
Betreff: [TRNSYS-users] Internal and external shading factors in Type 56
Hello all,
 
I'm using Type 56 to develop a model of a greenhouse which has controllable
inside screens to reduce incoming and outgoing radiation. I have used the
"internal shading factor" of the windows with an input variable to achieve
this, since the screens are actually on the inside of the greenhouse.
However, the internal shading device does not have quite the effect I
expected. It does not seem to reduce solar radiation hitting the zone, so
that temperatures rise very high on warm and sunny days. It does however
seem to reduce temperature loss at night, but this could be due to the
additional thermal resistance. By testing the "external shading factor"
instead, I found that this device has the effect I want, blocking out
radiation and keeping temperatures down on hot days. Can someone please tell
me if I have misunderstood the concept of internal shading? Does it not
prevent outside solar radiation from hitting the zone after passing through
the windows?
 
Best regards,
Knut Erik Enerstvedt
----------------------------------------------------------------------------
--------------------------
Meld deg på vårt nyhetsbrev på www.niva.no
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091112/878c693f/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: smime.p7s
Type: application/x-pkcs7-signature
Size: 7103 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091112/878c693f/attachment-0001.bin>
    
    
More information about the TRNSYS-users
mailing list