[TRNSYS-users] CO2 coupling with COMIS 3.2 and TRNSYS
keilholz, werner
werner.keilholz at cstb.fr
Mon May 18 05:58:02 PDT 2009
Hi Danny,
I'm not really an expert, but here's what I would do:
If your ventilation system is driven by TRNSYS components (equation cards, ...), you simply have to add an output (or several outputs) for CO2 to your type 157:
In Simulation Studio, open the parameters of type 157, and increase parameter 5 (Number of Outputs) by 1.
A new parameter will appear just below. In this new parameter, specify the CO2 you want to output. CO2 is usually pollutant #2.
(e.g. 02.01 is CO2 in zone 1, 02.02 in zone 2, 02.03 in zone3, 02.42 in zone 42, etc.).
Then connect these values to your equation(s) to compute the required fan speeds, which you feed back to type 157 (using parameter 2, 'number of links with schedules').
(creates a new parameter also, 'CIF Seq. Num. of link with TRNSYS schedule' -> give the position of the fan in the &-NET-LI section of the COMIS input file generated by Simulation Studio).
(The word 'schedule' is somewhat misleading here, what we mean is any value computed by a TRNSYS TYPE).
Werner
________________________________
De : danny roelofsen [mailto:dannyroelofsen at gmail.com]
Envoyé : vendredi 15 mai 2009 10:18
À : trnsys-users at cae.wisc.edu
Objet : [TRNSYS-users] CO2 coupling with COMIS 3.2 and TRNSYS
Dear TRNSYS Users,
I am trying to couple Trnsys and Comis to build a multizone model which can be controlled by CO2 concentrations. I can't figure out how to make the model's ventilation system react to the CO2 pollution that is generated by the occupants. Does anyone have a solution, or maybe an example-file so i can figure out how to do it?
I'm a new bee and I might have not explained the problem very well but any help is appreciated
Regards,
Danny Roelofsen, Student at Windesheim University, The Netherlands
************************************************************************************
This footnote confirms that this email message has been scanned by
PineApp Mail-SeCure for the presence of malicious code, vandals & computer viruses.
************************************************************************************
************************************************************************************
This footnote confirms that this email message has been scanned by
PineApp Mail-SeCure for the presence of malicious code, vandals & computer viruses.
************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090518/e975bcba/attachment-0001.htm>
More information about the TRNSYS-users
mailing list