Hello,
I'm a new user of TRNSYS and I have a problem with the windows.
I have a small room with only one window (and some necessary walls to satisfy TRNSYS requirements).
I have selected a window from the database, with U = 1.1 W/m².K and g = 0.609. The surface is 10 m². The window is horizontal.
A solar gains, I have 36 kJ/h.m², 100% diffuse. The temperature is the same on both sides (0°C).
I do expect that :
-         solar gains = 36*10 = 360 kJ/h.
-         solar gains that enters the room = 360*0.609 = 219 kJ/h.
-         heat losses = 1.1*10*3.600 = 39.6 kJ/h.K
-->  expected increase of temperature = 219/39.6 = 5.5 K.
However:
-         the calculated increase of temperature is only 2 K,
-         Qsoltr is only equal to 160 kJ/h, where I expected 219 kJ/h.
The same exercise with a glazing of type NoGlass (U = 5.68 W/m².K, g = 1) leads to an T° increase of  0 K where I would have expected:
 360 / (5.68*10*3.600) = 1.78 K.
Could you please tell me what's wrong?
(The model is attached, all files should be placed on C:)
Kind regards,
Nicolas Heijmans, Belgium
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090129/d5402232/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: TEST003.bui
Type: application/octet-stream
Size: 37846 bytes
Desc: TEST003.bui
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090129/d5402232/attachment-0002.obj>
-------------- next part --------------
An embedded and charset-unspecified text was scrubbed...
Name: MeteoPourTEST003.txt
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090129/d5402232/attachment-0001.txt>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: TEST003.tpf
Type: application/octet-stream
Size: 126875 bytes
Desc: TEST003.tpf
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090129/d5402232/attachment-0003.obj>
    
    
More information about the TRNSYS-users
mailing list