[TRNSYS-users] Time Inconsistency!

David Bradley bradley at tess-inc.com
Thu Oct 30 13:08:06 PDT 2008


Davide,
 When you specify your simulation time step in the Studio, I assume that 
you are changing the units from hours to minutes and then entering the 
corresponding value. What I would recommend is that you set the 
simulation time step units to "string" and enter the variable name "DELT"

Next, in the field at the bottom of the control cards window, paste the 
following two lines:

EQUATIONS 1
DELT = 10/60

(if you want to run with a different time step - 5 minutes, for example, 
then make the equation

DELT = 5/60

TRNSYS is trying to find two integers that when divided, give a value 
that is as close as possible to the decimal time step that was set. The 
Studio has a tendency to truncate time steps that are not entered in 
units of hours when it converts them back.

Kind regards,
 David


Davide Cali wrote:
> Dear TRNSYS users,
> I have a problem with my simulation, since it gives me an error, while 
> simulating, defined as "time inconsistency, check that time of last data 
> read and time of next data read are correctly connected".
> They of course are.
> The problem is I get this trouble just in the case my time step is 
> smaller then 10 minutes. with a 10 time step there are no problems.
> With a smaller time step (I simulate from May to September) the 
> simulation works till half July, then stucks.
> Thanks for attention and help,
> best regards,
> Davide
>
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************




More information about the TRNSYS-users mailing list