[TRNSYS-users] Variable for air extraction from one zone

David Bradley bradley at tess-inc.com
Tue Aug 29 13:12:46 PDT 2006


Antonio,
   I think an ideal method is to add a VENTILATION type to your zone. 
Type56 (in absence of an air flow model such as COMIS, CONTAM, or TRNFLOW) 
doesn't really care how much air you extract from the zone; it assumes that 
the pressure in the zone does not change so essentially it assumes that 
equal amounts of air are added and extracted. I would add the zone RH as a 
Type56 output and then make the VENTILATION stream temperature, RH, and air 
change rate into INPUTS, then connect the appropriate outputs of your 
circulation system to the Type56 inputs.
Kind regards,
  David


At 09:28 8/29/2006, Antonio Aguirre Glez. de San Pedro wrote:


>---------- Forwarded message ----------
>From: Antonio Aguirre Glez. de San Pedro 
><<mailto:aaguirresp at gmail.com>aaguirresp at gmail.com>
>Date: 28-ago-2006 10:47
>Subject: Variable for air extraction from one zone
>To: 
><mailto:TRNSYS-users-request at engr.wisc.edu>TRNSYS-users-request at engr.wisc.edu
>
>Hello all,
>I'm trying to recirculate the one zone air, cooling  it at the same time 
>(using Type56, Type32, Type92, Type3, Type 33, Type 2...). My main problem 
>is that I don't know how to generate one variable for the extraccion of 
>the air. I use the infiltration when I do the zone with prebid, but I 
>think is not the good way.
>Thanks in Advance
>Antonio Aguirre
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20060829/d3865d42/attachment-0001.htm>


More information about the TRNSYS-users mailing list