Antonio,<br>
I think an ideal method is to add a VENTILATION type to your zone.
Type56 (in absence of an air flow model such as COMIS, CONTAM, or
TRNFLOW) doesn't really care how much air you extract from the zone; it
assumes that the pressure in the zone does not change so essentially it
assumes that equal amounts of air are added and extracted. I would add
the zone RH as a Type56 output and then make the VENTILATION stream
temperature, RH, and air change rate into INPUTS, then connect the
appropriate outputs of your circulation system to the Type56 inputs.<br>
Kind regards,<br>
David<br><br>
<br>
At 09:28 8/29/2006, Antonio Aguirre Glez. de San Pedro wrote:<br><br>
<br>
<blockquote type=cite class=cite cite="">---------- Forwarded message
----------<br>
From: <b>Antonio Aguirre Glez. de San Pedro</b>
<<a href="mailto:aaguirresp@gmail.com">aaguirresp@gmail.com</a>><br>
Date: 28-ago-2006 10:47<br>
Subject: Variable for air extraction from one zone<br>
To:
<a href="mailto:TRNSYS-users-request@engr.wisc.edu">
TRNSYS-users-request@engr.wisc.edu</a><br><br>
Hello all,<br>
I'm trying to recirculate the one zone air, cooling it at the same
time (using Type56, Type32, Type92, Type3, Type 33, Type 2...). My main
problem is that I don't know how to generate one variable for the
extraccion of the air. I use the infiltration when I do the zone with
prebid, but I think is not the good way. <br>
Thanks in Advance<br>
Antonio Aguirre<br><br>
<br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY
2916 Marketplace Drive - Suite 104 <br>
Partner
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages:
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>
and
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>