[Equest-users] Tip for unmet heating hours in VAV systems
    Pasha Korber-Gonzalez 
    pasha.pkconsulting at gmail.com
       
    Fri Sep 16 12:23:04 PDT 2011
    
    
  
Thanks Bill--I think this will be helpful.  I currently have a baseline
model with whacked underheated hours and with upsizing ratios and autosized
calcs nothing is changing for me.  I will try this input adjustment and see
if it works.
Thanks for sharing!
Pasha
On Fri, Sep 16, 2011 at 8:33 AM, Bishop, Bill <wbishop at pathfinder-ea.com>wrote:
>  Thought I’d share a tip for addressing unmet heating hours in VAV systems
> using eQUEST 3.64.****
>
> ** **
>
> eQUEST 3.64 adds the HMAX-FLOW-RATIO keyword in System -> Fans -> Flow
> Parameters. The default value is the greater of the fan MIN-FLOW-RATIO and
> 0.5, but this value is determined by the program and you don’t see it when
> you look at the Flow Parameters tab. Entering a value of 1.0 corrected an
> unmet heating hours problem for me that appeared when I opened a model in
> 3.64 that I originally created in 3.63. This works for both VAVS and PVAVS
> system types.****
>
> ** **
>
> Regards,****
>
> Bill****
>
> ** **
>
> [image: Senior Energy Engineer]****
>
> ** **
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110916/0c78a897/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110916/0c78a897/attachment.jpeg>
    
    
More information about the Equest-users
mailing list