[Equest-users] Tip for unmet heating hours in VAV systems
Bishop, Bill
wbishop at pathfinder-ea.com
Fri Sep 16 07:33:55 PDT 2011
Thought I'd share a tip for addressing unmet heating hours in VAV
systems using eQUEST 3.64.
eQUEST 3.64 adds the HMAX-FLOW-RATIO keyword in System -> Fans -> Flow
Parameters. The default value is the greater of the fan MIN-FLOW-RATIO
and 0.5, but this value is determined by the program and you don't see
it when you look at the Flow Parameters tab. Entering a value of 1.0
corrected an unmet heating hours problem for me that appeared when I
opened a model in 3.64 that I originally created in 3.63. This works for
both VAVS and PVAVS system types.
Regards,
Bill