[Equest-users] Tip for unmet heating hours in VAV systems
    Bishop, Bill 
    wbishop at pathfinder-ea.com
       
    Fri Sep 16 07:33:55 PDT 2011
    
    
  
Thought I'd share a tip for addressing unmet heating hours in VAV
systems using eQUEST 3.64.
 
eQUEST 3.64 adds the HMAX-FLOW-RATIO keyword in System -> Fans -> Flow
Parameters. The default value is the greater of the fan MIN-FLOW-RATIO
and 0.5, but this value is determined by the program and you don't see
it when you look at the Flow Parameters tab. Entering a value of 1.0
corrected an unmet heating hours problem for me that appeared when I
opened a model in 3.64 that I originally created in 3.63. This works for
both VAVS and PVAVS system types.
 
Regards,
Bill
 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110916/0381af6b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110916/0381af6b/attachment.jpeg>
    
    
More information about the Equest-users
mailing list